1. Welcome to the new and improved Building Code Forum. We appreciate you being here and hope that you are getting the information that you need concerning all codes of the building trades. This is a free forum to the public due to the generosity of the Sawhorses, Corporate Supporters and Supporters who have upgraded their accounts. If you would like to have improved access to the forum please upgrade to Sawhorse by clicking here: Upgrades
    Dismiss Notice

Unvented Crawl Space

Discussion in 'Residential Foundation Codes' started by Bama dav, Jul 26, 2013.

  1. Sifu

    Sifu Gold Member

    Joined:
    Sep 3, 2011
    Messages:
    1,162
    Likes Received:
    119
    Don't use the foam. Or use the foam with prescriptive ignition or thermal barrier. There are other ways to insulate. I have had that conversation and emails with ICC. I think it boils down to the fact that either the code hasn't caught up to the industry or the industry got ahead of itself.....or a little of both.
     
  2. Bama dav

    Bama dav Bronze Member

    Joined:
    Jun 11, 2012
    Messages:
    30
    Likes Received:
    0
    Yes, that is what the fiberglass guys do. They use a rigid fiberboard insulation (r5).
     
  3. Daddy-0-

    Daddy-0- Moderator

    Joined:
    Oct 24, 2009
    Messages:
    855
    Likes Received:
    0
    Have them apply for a modification or follow the IRC. All you can do if they will not bend on the install. Time for them to do the homework in my opinion.
     
  4. Rider Rick

    Rider Rick Silver Member

    Joined:
    Oct 19, 2009
    Messages:
    468
    Likes Received:
    1
    2 inch is R-10 and I think this will meet code for basement stem walls and under slab with 6 mil vapor barrier.
     
  5. jar546

    jar546 *****istrator

    Joined:
    Oct 16, 2009
    Messages:
    7,046
    Likes Received:
    518
    There are some rigid foam boards that are approved for use inside crawlspaces but not basement walls. There are some rigid foam boards that are allowed in both and some that are not allowed in either. You have to check each specific brand and type to see.
     
  6. Rider Rick

    Rider Rick Silver Member

    Joined:
    Oct 19, 2009
    Messages:
    468
    Likes Received:
    1
    As long as the rigid form boards on the inside of the basement wall are covered with Sheetrock that should meet code.
     
  7. tmurray

    tmurray Sawhorse

    Joined:
    Jun 10, 2011
    Messages:
    1,662
    Likes Received:
    439
    Is it a 2lb or 1/2 lb product? Is the floor of the crawl space concrete or dirt? If concrete was 6mil poly installed?
     
  8. Francis Vineyard

    Francis Vineyard Sawhorse

    Joined:
    Jan 1, 2010
    Messages:
    3,113
    Likes Received:
    417
    Is an ignition barrier; prescriptive or approved coating required with Icynene LD-C-50 in accordance with Section 4.4.2.3 in unvented crawl space per Section 4.4.2?

    Mr. Vineyard,

    In response to your voicemail please see the attached ESR 1826. Section 4.4.2.3 allows for the use of this foam in an unvented crawlspace provided the conditions in 4.4.2 are followed and the thickness of the foam noted in 4.4.2.3 is not exceeded without the need for a prescriptive ignition barrier or coating material.

    Please do not hesitate to contact me should you require any additional assistance or clarification.

    Best Regards

    Paul W

    Building Science Technologist, ICYNENE

     
    #28 Francis Vineyard, Jul 30, 2013
    Last edited by a moderator: Jul 30, 2013
  9. Bama dav

    Bama dav Bronze Member

    Joined:
    Jun 11, 2012
    Messages:
    30
    Likes Received:
    0
    Francis,again I agree but 4.4.2 # 6 requires foundation vents per 408.1. So move on to enclosed crawlspace 408.3( I think) requires a air pathway to the common area that ESR 1826 #3 doesn't allow. The gentleman I spoke with at ICC said there was a problem with this conflict and he said it was on next month agenda to try and resolve.
     
  10. Bama dav

    Bama dav Bronze Member

    Joined:
    Jun 11, 2012
    Messages:
    30
    Likes Received:
    0
    Sorry ESR 1826 4.4.2 #3 doesn't allow it.
     
  11. Francis Vineyard

    Francis Vineyard Sawhorse

    Joined:
    Jan 1, 2010
    Messages:
    3,113
    Likes Received:
    417
    The way I see it the conditioned crawl communicates with the interior and has been interpreted to allow an ignition barrier instead of thermal; R408.3 Unvented Crawl Space

    Similarly a allowed in cases with up to 2 inches of styrofoam; (rigid board insulation) the ESR under specific approval permits this product up to 3½ in thickness without an ignition barrier in unvented crawl spaces.

    Francis

     
    #31 Francis Vineyard, Jul 30, 2013
    Last edited by a moderator: Jul 30, 2013
  12. Francis Vineyard

    Francis Vineyard Sawhorse

    Joined:
    Jan 1, 2010
    Messages:
    3,113
    Likes Received:
    417
    Let me know what I'm missing.

    The ESR is written much like the IRC; general statements that are most restrictive followed by exceptions.

    Section 4.3.2 the alternative coating can be applied if the thickness on walls does not exceed 6 inches in accordance with IRC specific approval; ESR section 6.3: NFPA 286.

    Section 4.4.2 requires a prescriptive ignition barrier if the air circulates to other parts of the building, but in accordance with section 5.3 of this ESR and the ICC interpretation does not require a thermal barrier for unvented crawl spaces.

    Section 4.4.2.3 does not require the alternative coating or prescriptive ignition barrier if the thickness does not exceed 3½ inches.

    Francis
     
  13. Sifu

    Sifu Gold Member

    Joined:
    Sep 3, 2011
    Messages:
    1,162
    Likes Received:
    119
    What I found is this;

    The code allows an unvented crawlspace when it circulates air to the common area.

    The code allows foam insulation when installed in accordance with the mfr specs.

    MOST Mfr specs (and tests performed) did not anticipate the "circultated air with the common space" requirement.

    Intumescent coatings provide an equivalent ignition or thermal barrier depending on the product.

    MOST Intumescent coatings are irrelevent because they don't over-rule the stipulated conditions in the ES reports.

    This is a problem that must be worked out between the industry and the code making body, not field inspectors.

    I have found a lot of conflicts within the ES reports, a lot of circular references. I am leaving it up to the industry and/or the code to work it out. If we spend too much time doing their job they won't be forced to rectify the problems they have created, either by their actions or in-actions. I figure if I can keep on turning down these things they can't seem to make clear, they will figure out a way to make them clear.
     
  14. jar546

    jar546 *****istrator

    Joined:
    Oct 16, 2009
    Messages:
    7,046
    Likes Received:
    518
    But,......not all foam is required to be.
     
  15. Rider Rick

    Rider Rick Silver Member

    Joined:
    Oct 19, 2009
    Messages:
    468
    Likes Received:
    1
    That's good then.
     
  16. peach

    peach Sawhorse

    Joined:
    Oct 17, 2009
    Messages:
    2,834
    Likes Received:
    2
    build it like a mini-basement and you should be good.
     