Not sure about that. Or perhaps to eliminate the pick & choose I classify it as S2 and just build above that? brudges, how about a little more information? Sure would help.cda said:1 as long as they meet minimum for what they are actualy doing2 if they design to higher standard, then they need to meet all the requirements if that higher standard, not pick and chose
Run, it's contagious.TJacobs said:Yes; it is the other way around I would have a problem.
Even if F1 is classified as moderate-hazard and F2 as low-hazard, F1 is not necessarily always more restrictive than F2. For example F1 does not require separation from B or M occupancy groups, while F2 requires the separation (Table 508.3.3). If the space function falls under F2 occupancy category then you shall call it F2. The “higher standard” approach would be acceptable if your space complies with all the Building Code Sections for Both F1 and F2 occupancy groups, not only F1.Suppose you had a beverage plant which would be F2. Would you allow it to be classified as the more restrictive F1?
I do understand the purpose of separation between F2 and B or M. That’s why I call F2 more restrictive (needs better protection) than F1. My point is that if you are brewing in one space (F2) and selling at adjacent space (M), then you need the separation between F2 and M. You can’t just rename the actual F2 occupancy group to F1 to get rid of the separation.The fire separation between F2 and B is to protect the low hazard F2 from the moderate hazard B.Not vice versa.
So would you say that it’s OK to produce beer and explosives within the same building as long as entire building complies with H1 occupancy requirements?brudgers said:A space designed as F2 requires protection from a space designed as B because it may be constructed with a larger area and less fire resistance than one constructed as F1 (see tables 503, 602, 705.4, and 706.3.9) and without sprinklers regardless of size allowed by table 503 (see section 903.2).You are misunderstanding the reason for the protection of F2 from B.