The way the stupid code change went in, a single piece of upholstered furniture requires the entire building to be sprinkelred. I spoke against this at the code hearings (all of them) and the stupid thing still passed. There is no latitude in the way the code text is worded. It's dumb and needs a variance.
I wish all you level headed folks would have been at the code hearings so we could shoot this down.
mtlogcabin,
I don't know who the instructor was but he/she was obviously telling you what the thinking was for the code chaneg not what it actually says.
The 2012 will be better:
903.2.7 (IBC [F] 903.2.7
Group M. An automatic sprinkler system shall be provided throughout buildings containing a Group M occupancy where one of the following conditions exists:
1. Where a Group M fire area exceeds 12,000 square feet (1115 m2);
2. Where a Group M fire area is located more than three stories above grade plane; or
3. Where the combined area of all Group M fire areas on all floors, including any mezzanines, exceeds 24,000 square feet (2230 m2). ; or
4. Where a Group M occupancy that is used for the display and sale of upholstered furniture or mattresses exceeds 5,000 square feet (464 m2).
903.2.9 (IBC [F] 903.2.9)
Group S-1. An automatic sprinkler system shall be provided throughout all buildings containing a Group S-1 occupancy where one of the following conditions exists:
1. A Group S-1 fire area exceeds 12,000 square feet (1115 m2);
2. A Group S-1 fire area is located more than three stories above grade plane; or
3. The combined area of all Group S-1 fire areas on all floors, including any mezzanines, exceeds 24,000 square feet (2230 m2).
4. A Group S-1 fire area used for the storage of commercial trucks or buses where the fire area exceeds 5,000 square feet (464 m2).
5. A Group S-1 occupancy that is used for the storage of upholstered furniture or mattresses exceeds 2,500 square feet (232 m2).