I am an architect in Indiana. I am working on a 12,000 SF +/- type V-A church project. The owner does not want to install a sprinkler. Indiana is presently governed by the 2012 IBC with Indiana amendments. Indiana has an amendment which allows for a fire area to be up to 7,000 regardless of occupant load, so I broke the building into three wings (Fellowship, Sanctuary, and Education), which are separated by a 2-hour fire barrier to create three separate compliant Fire Areas. Although there was some push back in the beginning from State and Local plan reviewers, I have gotten them to accept that this is possible, per the amendment (because otherwise it simply is NOT).
The issue becomes finding UL or other tested assemblies to show compliance with the type V-A and fire barrier provisions, which require all structural elements to be one-hour min. or two-hour fire rated, respectively. I have several different types of assemblies:
The reviewer was kind enough to explain to me that using the CH 7 prescriptive fire resistance is easier than finding UL or other tested assemblies in many cases. I basically nodded my head and said "OK, I will look into that!" But I have no idea how to use CH 7 for "building" one and two-hour fire rated assemblies that can show compliance. Does anyone know of any online resources I can access OR has anyone done this that explain how CH 7 can be used to simply show compliance with basic one and two hour fire-rated assemblies for combustible type V-A construction?
The weather is breaking and this client is going to want to start building soon. This is the last hurdle, and I really need to get this project finalized and through the plan review next week! Many thanks in advance for any insight. I love using this site to further my knowledge about the design and construction industry.
The issue becomes finding UL or other tested assemblies to show compliance with the type V-A and fire barrier provisions, which require all structural elements to be one-hour min. or two-hour fire rated, respectively. I have several different types of assemblies:
- The exterior bearing walls are required to be one-hour fire rated due to being type V-A construction. In practice, this is typically achieved with 5/8" type X drywall on the interior (protected) side. Note: We have no property line issues, so protection from the exterior is not required.
- The roof is constructed with flat and scissor trusses, thus this also requires a one-hour fire rating from the interior.
- The church features a mezzanine level for the sound booth, so we now have to fire protect the floor framing for the mezzanine, which consist of 12" open web wood trusses.
- In the fellowship wing, we have a clear span space which will have steel columns and beams supporting the trusses, thus the steel structure needs to be one-hour fire rated.
- Two-hour fire barriers to separate the fire areas.
The reviewer was kind enough to explain to me that using the CH 7 prescriptive fire resistance is easier than finding UL or other tested assemblies in many cases. I basically nodded my head and said "OK, I will look into that!" But I have no idea how to use CH 7 for "building" one and two-hour fire rated assemblies that can show compliance. Does anyone know of any online resources I can access OR has anyone done this that explain how CH 7 can be used to simply show compliance with basic one and two hour fire-rated assemblies for combustible type V-A construction?
The weather is breaking and this client is going to want to start building soon. This is the last hurdle, and I really need to get this project finalized and through the plan review next week! Many thanks in advance for any insight. I love using this site to further my knowledge about the design and construction industry.