2012 IBC
[A] 104.9 Approved materials and equipment.
Materials, equipment and devices approved by the building official shall be constructed and installed in accordance with such approval.
[A] 104.9.1 Used materials and equipment.
The use of used materials which meet the requirements of this code for new materials is permitted. Used equipment and devices shall not be reused unless approved by the building official.
2012 IRC
R104.9 Approved materials and equipment.
Materials, equipment and devices approved by the building official shall be constructed and installed in accordance with such approval.
R104.9.1 Used materials and equipment.
Used materials, equipment and devices shall not be reused unless approved by the building official.
2012 IMC
Hydronic piping
1202.2 Used materials.
Reused pipe, fittings, valves or other materials shall be clean and free of foreign materials and shall be approved by the code official for reuse.
2012 IPC is silent on used materials
[A] 104.9 Approved materials and equipment.
Materials, equipment and devices approved by the building official shall be constructed and installed in accordance with such approval.
[A] 104.9.1 Used materials and equipment.
The use of used materials which meet the requirements of this code for new materials is permitted. Used equipment and devices shall not be reused unless approved by the building official.
2012 IRC
R104.9 Approved materials and equipment.
Materials, equipment and devices approved by the building official shall be constructed and installed in accordance with such approval.
R104.9.1 Used materials and equipment.
Used materials, equipment and devices shall not be reused unless approved by the building official.
2012 IMC
Hydronic piping
1202.2 Used materials.
Reused pipe, fittings, valves or other materials shall be clean and free of foreign materials and shall be approved by the code official for reuse.
2012 IPC is silent on used materials