Using the 2024 IRC and NFPA 31 for Combustion Air Requirements

Combustion air is critical for the safe and efficient operation of oil-fired and solid fuel-fired appliances. The 2024 International Residential Code (IRC) and NFPA 31: Standard for the Installation of Oil-Burning Equipment provide the necessary guidelines to ensure that appliances receive adequate air for combustion while maintaining proper ventilation and safety standards. Understanding how these codes work together is essential for code officials, contractors, and inspectors responsible for the installation and inspection of combustion appliances.

IRC Chapter 17 Overview

Chapter 17 of the 2024 IRC applies only to oil-fired and solid fuel-fired appliances, excluding gas-fired appliances, which fall under Chapter 24. Key requirements include:
  1. Manufacturer’s Instructions Compliance
    • Solid fuel-burning appliances must follow the manufacturer’s guidelines for combustion air.
    • Oil-fired appliances must comply with NFPA 31 standards for combustion air.
  2. Location Restrictions
    • In flood hazard areas, combustion air openings must be above the design flood elevation per IRC Section R306.
The IRC provides broad guidelines but references NFPA 31 for the specifics of oil-burning appliance installations.

NFPA 31: Air for Combustion and Ventilation

NFPA 31 expands on the combustion air requirements for oil-burning appliances with detailed criteria for air supply based on appliance location, building construction, and ventilation needs. Key aspects include:

1. Basic Requirements (Section 5.2)

  • Appliances must be installed in locations with adequate air for combustion and ventilation.
  • Worst-case depressurization testing is required before commissioning the equipment.
  • Outside air must be introduced if infiltration is insufficient due to tight building construction.

2. Combustion Air Methods

NFPA 31 provides three primary methods to ensure proper air supply:
  1. Unconfined Spaces (Section 5.3):
    • In conventional buildings, normal infiltration may provide sufficient air.
    • If insufficient, openings must provide 1 in² per 5000 Btu/hr.
  2. Confined Spaces (Section 5.4):
    • Two openings are required: high and low within the space.
    • If drawing air from indoors, 1 in² per 1000 Btu/hr is required.
    • If drawing air from outdoors, vertical ducts need 1 in² per 4000 Btu/hr, and horizontal ducts need 1 in² per 2000 Btu/hr.
  3. Mixed Air Supply (Section 5.4.3):
    • Combustion air from outdoors; ventilation air from inside the building.

3. Special Considerations

  • Louvers and Grilles (Section 5.6):
    • The free area must account for blocking effects.
    • Metal grilles are assumed to have 75% free area, while wood louvers only provide 25%.
  • Engineered Installations (Section 5.7):
    • Special methods may be approved by the authority having jurisdiction if they ensure adequate combustion air.

Key Differences Between the IRC and NFPA 31

FeatureIRC (2024)NFPA 31 (2024)
ScopeResidential applications onlyResidential, commercial, and industrial
Air supply methodsManufacturer or NFPA complianceDetailed air volume and placement specs
Confined space rulesGeneral guidelinesSpecific opening size requirements
Testing requirementsNot explicitly statedRequires depressurization testing
By integrating both the IRC and NFPA 31, professionals can ensure code compliance and the safe operation of oil-burning appliances in various building types.

Quiz: 2024 IRC and NFPA 31 Combustion Air Requirements

1. According to the 2024 IRC, which appliances fall under Chapter 17 for combustion air requirements?
A. Gas-fired appliances
B. Electric heating systems
C. Oil-fired and solid fuel-fired appliances
D. All heating appliances
2. NFPA 31 requires combustion air ducts to have what minimum cross-sectional area compared to the free area of the opening?
A. 50%
B. Equal to the free area
C. 75%
D. 200%
3. When are secondary (emergency overflow) drains or scuppers not required under the IRC?
A. When the roof slope exceeds 1/4 unit vertical in 12 units horizontal
B. When the roof provides positive drainage
C. When the roof covering is new
D. When the building is less than 5000 square feet
4. How much free area is required for combustion air openings in unconfined spaces according to NFPA 31?
A. 1 in² per 4000 Btu/hr
B. 1 in² per 2000 Btu/hr
C. 1 in² per 1000 Btu/hr
D. 1 in² per 5000 Btu/hr
5. According to NFPA 31, which scenario would not require additional outdoor air for combustion?
A. A tightly sealed building with minimal infiltration
B. A conventionally built home with adequate infiltration
C. A commercial boiler room
D. An underground basement installation
6. In a confined space where combustion air is drawn from indoors, how many openings must be provided?
A. One at the ceiling level
B. One at the floor level
C. Two – one high and one low
D. None if windows are present
7. What is the minimum free area required for combustion air openings in confined spaces where air is drawn from outside via vertical ducts per NFPA 31?
A. 1 in² per 1000 Btu/hr
B. 1 in² per 2000 Btu/hr
C. 1 in² per 4000 Btu/hr
D. 1 in² per 5000 Btu/hr
8. In flood hazard areas, where must combustion air openings be located per the IRC?
A. Below the base flood elevation
B. At or above the elevation required in R306
C. At the highest point of the structure
D. Below windows and doors
9. What is the purpose of performing a depressurization test under NFPA 31 requirements?
A. To determine the structural integrity of the appliance
B. To check for leaks in the fuel system
C. To ensure proper draft for combustion
D. To verify insulation compliance
10. Under NFPA 31, what type of appliance installation requires compliance with Section 5.5?
A. Residential installations
B. Industrial and commercial installations
C. Mobile homes
D. Temporary installations
 
f you’re working with oil-fired or solid fuel-fired appliances, it’s important to follow the 2024 IRC and NFPA 31 for proper combustion air requirements. The IRC gives general guidelines, while NFPA 31 goes into more detail, especially for confined spaces and ventilation methods. If the building is tightly sealed, you might need to bring in outside air.
 
f you’re working with oil-fired or solid fuel-fired appliances, it’s important to follow the 2024 IRC and NFPA 31 for proper combustion air requirements. The IRC gives general guidelines, while NFPA 31 goes into more detail, especially for confined spaces and ventilation methods. If the building is tightly sealed, you might need to bring in outside air.
Isn't that exactly what the article said?
 
2018 Energy Code is specific for fireplaces. I could not find a reference to other solid fuel appliances.

R402.4.2 Fireplaces.
New wood-burning fireplaces shall have tight-fitting flue dampers or doors, and outdoor combustion air. Where using tight-fitting doors on factory-built fireplaces listed and labeled in accordance with UL 127, the doors shall be tested and listed for the fireplace.
 