VA Construction "floor construction"?

steveray

SAWHORSE
Joined
Nov 25, 2009
Messages
13,748
Location
West of the river CT
Not that I think it matters but R-2 apartments, VA proposed construction....

Just wanted to see how everyone is handling stair stringers in VA construction? Is it a joist? Is it a floor or secondary member? Does it need to be rated? Does it matter if it is inside an exit enclosure or not?
 
Last edited by a moderator:
The commentary for stairway construction section in chapter 10;

"In keeping with the different levels of fire protection provided by each of the five basic types of construction designated in Chapter 6, the materials used for stairway construction must meet the appropriate combustibility/noncombustibility requirements indicated in Section 602 for the particular type of construction of the building in which the stairway is located. This is required whether or not the stair is part of the required means of egress. Any structure supporting the stairway and the stairway enclosure must be fire-resistance rated consistent with the construction type; however, the stairway components inside the enclosure need only comply with the material limits for the type of construction.

If desired, wood handrails may be used on the basis that the fuel load contributed by this combustible component of stairway construction is insignificant and will not pose a fire hazard."

Chapter 14 Balconies and Similar Projection address the construction for exterior stairs;

"Balconies, porches, decks, supplemental exterior stairs and similar appendages in buildings of Types I and II construction are required to be constructed of noncombustible materials in order to prevent fire involvement and fire spread up or along the exterior of a noncombustible building. In buildings of Types III, IV and V construction, the use of combustible materials for these elements is permitted."
 
Thanks Guys....Struggling a bit with the stairs being a secondary member or floor construction(I know they are not primary) which still requires the 1 hr rating in VA construction. Understanding that if you had that fire in the stairs, you are pretty much SOL...The FV commentary makes that much sense, but I will have to stew on it a bit more...
 