Vapor barrier under slab

90limited

REGISTERED
Joined
May 10, 2022
Messages
2
Location
South west florida
We are building in SWFL. They are tears in the vapor barrier. It is almost a foot short of the stem wall in place and a few places with no plastic at all. Out builder thinks this is ok. I do not. Thoughts?
 
Slab below grade? You mentioned stem walls so it is assumed that the slab is below grade requing VB

If below grade, VB should be overlapped a minimum of 6-inches and should not be short of the stem wall. There will be some holes around stubbed piping but there should be minimal areas of openings and large areas can be resolved with additional VB.

*See IRC 506.2.3 or FL codes if applicable.
 
The inspector should require it to be installed correctly. What your builder thinks is okay is irrelevant? What you describe is not code compliant. Talk to the building department and express your concerns. Depending on what jurisdiction you are in the inspection could be onsite or a virtual inspection which some things don't show up on.
 