Scenerio: Designer proposing a 2 story non seperated mixed use A2/B VB construction. The bottom floor has 6200 sq ft A2 and the top floor (proposed) is 6200 sq ft use group B. I am saying no, the A2 requires sprinklers if it exceeds 5000 sq ft and therefore you cannot also claim the building is sprinkled and so you can add a second floor for the sprinkler increase.
I have suggested calling this a seperated mixed use, break the A@ fire area to below 5000 sq ft and you may then sprinkle the building and gain the story increase.
Thoughts please and as always thanks.
I have suggested calling this a seperated mixed use, break the A@ fire area to below 5000 sq ft and you may then sprinkle the building and gain the story increase.