Ok type IDr. J said:What is a commercial vent a hood?
just trying to give an exampleDr. J said:There are a whole lot of requirements for a Type 1 Commercial Kitchen Hood Duct, see IMC ch 5. Among the requirement is that the duct be in a rated enclosure from the hood to the exterior. The enclosed duct is essentially a shaft, and one of the purposes is to extend the fire area of origin directly to the exterior. Thus any penetrations of fire restive construction is inherently protected by that enclosure/shaft.The Fire Wall question is interesting. A Fire Wall (as opposed to a Fire Barrier) creates two separate buildings. Why do you have a Fire Wall in a restaurant? Recall that a Fire Wall is expected to be structurally independent of either building, allowing either side to collapse while the Fire Wall remains standing. How would you create an enclosure that could do that? Probably should avoid a Fire Wall, stay in the building you start in.
doe any of this apply???JBI said:There is an exception, but it is not applicable to your project/scenario.607.6 Horizontal assemblies.
Penetrations by air ducts of a floor, floor/ceiling assembly or the ceiling membrane of a roof/ceiling assembly shall be protected by a shaft enclosure that complies with Section 713 and Sections 717.6.1 through 717.6.3 of the International Building Code or shall comply with Sections 607.6.1 through 607.6.3.
607.6.1 Through penetrationsIn occupancies other than Groups I-2 and I-3, a duct constructed of approved materials in accordance with Section 603 that penetrates a fire-resistance-rated floor/ceiling assembly that connects not more than two stories is permitted without shaft enclosure protection provided that a listed fire damper is installed at the floor line or the duct is protected in accordance with Section 714.4 of the International Building Code. For air transfer openings, see Exception 7, Section 712.1.8 of the International Building Code.
No down to if say four floor buildingJBI said:Basically the options are enclose in a shaft or provide dampers. (unless of course your point is to keep asking about random code sections until you get the answer you want?)