• Welcome to the new and improved Building Code Forum. We appreciate you being here and hope that you are getting the information that you need concerning all codes of the building trades. This is a free forum to the public due to the generosity of the Sawhorses, Corporate Supporters and Supporters who have upgraded their accounts. If you would like to have improved access to the forum please upgrade to Sawhorse by first logging in then clicking here: Upgrades

Vent Pipe Slope

Mech

Registered User
Joined
Oct 30, 2009
Messages
1,037
Location
Eastern PA
What is the minimum slope for vents under the 2009 IPC and the 2015 National Standard Plumbing Code?
Is any positive slope adequate or must the vent pipe slope follow the slope for drainage pipe?

Thanks in advance.


2009 IPC Section 905.2 Grade
All vent and branch vent pipes shall be so graded and connected as to drain back to the drainage pipe by gravity.

2015 NSPC Section 12.6.1 Vent Slope
Vent and branch vent pipes shall be free from drops and sags and be sloped and connected as to drain by gravity to the drainage system.
 
I would say positive slope would be any minimum or maximum slope so long as condensation, rain or other liquid could reasonably drain into the sanitary drainage system.
 
  • Like
Reactions: JBI
@ ~ @

Also, see Section 911.3 [ `09 IPC ] - Slope and size of horizontal branch:
"The maximum slope of the vent section of the horizontal branch drain
shall be one unit vertical in twelve units horizontal ( 8 per cent slope ).
The entire length of the vent section of the horizontal branch drain
shall be sized for the total drainage discharge to the branch."



@ ~ @
 
  • Like
Reactions: JBI