In looking thru the `10 ADA SAD, there is no requirement to have Vertical
Grab Bars ( VGB's ) installed.........Also, in looking in the `09 ANSI A117.1,
at Section 609.4.1, ...the language seems to indicate "choice" of installing
Horizontal Grab Bars ( HGB's ), or if VGB's are installed they must comply
with the sections listed in # 2.
From the `09 ANSI A117.1, Section 609.4.1 - Position of Grab Bars:
"609.4.1 - General: Grab bars shall be installed in a horizontal position,
33 inches (840 mm) minimum and 36 inches (915 mm) maximum above
the floor measured to the top of the gripping surface or shall be installed
as required by Items 1 through 3.
1. The lower grab bar on the back wall of a bathtub shall comply with
Section 607.4.1.1 or 607.4.2.1.
2. Vertical grab bars shall comply with Sections 604.5.1, 607.4.1.2.2,
607.4.2.2, and 608.3.1.2.
3. Grab bars at water closets primarily for children's use shall comply
with Section 609.4.2"
So, ...is there a choice between installing HGB's ONLY, or to actually install
VGB's as well, or something else ?
Thanks for any input !
< @ < @
In looking thru the `10 ADA SAD, there is no requirement to have Vertical
Grab Bars ( VGB's ) installed.........Also, in looking in the `09 ANSI A117.1,
at Section 609.4.1, ...the language seems to indicate "choice" of installing
Horizontal Grab Bars ( HGB's ), or if VGB's are installed they must comply
with the sections listed in # 2.
From the `09 ANSI A117.1, Section 609.4.1 - Position of Grab Bars:
"609.4.1 - General: Grab bars shall be installed in a horizontal position,
33 inches (840 mm) minimum and 36 inches (915 mm) maximum above
the floor measured to the top of the gripping surface or shall be installed
as required by Items 1 through 3.
1. The lower grab bar on the back wall of a bathtub shall comply with
Section 607.4.1.1 or 607.4.2.1.
2. Vertical grab bars shall comply with Sections 604.5.1, 607.4.1.2.2,
607.4.2.2, and 608.3.1.2.
3. Grab bars at water closets primarily for children's use shall comply
with Section 609.4.2"
So, ...is there a choice between installing HGB's ONLY, or to actually install
VGB's as well, or something else ?

Thanks for any input !
< @ < @