I have a multi-story building with mixed uses. The first floor is retail, the second floor is mixed with retail, assembly (fitness center) and office. The third floor, which is only 1/3 of the footprint of the other two floors is office.
The first and second floor are open to each other in the building of the building with a common entry which has a grand staircase as well as two elevators. The stair is required for egress.
The person reviewing this project for permit is insisting that the two story opening is an atrium and does not qualify for a vertical opening. I cannot find anything in the IBC which restricts the opening size of the vertical opening. This project is being reviewed under the 2009 IBC. Section 708.2 exception #11 allows for a floor opening created by an unenclosed stair if it complies with Section 1016.1 exception #3 or 4. I believe we meet both exceptions #3 and 4 in 1016.1 as we have at least two means of egress in other areas of the building serving all floors. Therefore I believe the stair can be an exit access stair and not have to be enclosed. While the area in question is rather large, again, I cannot find any code language that limits the area of that opening.
I've looked in NFPA 101 and the best I can find there is in section 36.3.1 which allows for vertical openings in retail occupancies between any two floors and among the street floor and first adjacent floor with no size limitation on the opening.
I even called ICC to get a staff interpretation and was told I was correct. However, I got sent an email this morning where the plans examiner said I had an attitude and had no clue what I was talking about.
Am I way off base here? If so, please point me in a direction to help me better understand as I thought I understood this.
Thanks.
The first and second floor are open to each other in the building of the building with a common entry which has a grand staircase as well as two elevators. The stair is required for egress.
The person reviewing this project for permit is insisting that the two story opening is an atrium and does not qualify for a vertical opening. I cannot find anything in the IBC which restricts the opening size of the vertical opening. This project is being reviewed under the 2009 IBC. Section 708.2 exception #11 allows for a floor opening created by an unenclosed stair if it complies with Section 1016.1 exception #3 or 4. I believe we meet both exceptions #3 and 4 in 1016.1 as we have at least two means of egress in other areas of the building serving all floors. Therefore I believe the stair can be an exit access stair and not have to be enclosed. While the area in question is rather large, again, I cannot find any code language that limits the area of that opening.
I've looked in NFPA 101 and the best I can find there is in section 36.3.1 which allows for vertical openings in retail occupancies between any two floors and among the street floor and first adjacent floor with no size limitation on the opening.
I even called ICC to get a staff interpretation and was told I was correct. However, I got sent an email this morning where the plans examiner said I had an attitude and had no clue what I was talking about.
Am I way off base here? If so, please point me in a direction to help me better understand as I thought I understood this.
Thanks.