Thus wall studs and/or walls are limited to twelve feet.......Individual walls or walls studs shall be permitted to exceed these limits as permitted by Chapter 6 provisions, providedstory heights are not exceeded. An engineered design shall be provided for the wall or wall framing members when they
exceed the limits of Chapter 6. Where the story height limits are exceeded, an engineered design shall be provided in accordance
with the International Building Code for the overall wind and seismic force resisting systems.
Yes I could use spray on/in cell foam insulation but the question really becomes one of how much 1/2" plywood sheathing can I use in conjunction with the 2009 IECC requirement for the R-5/R-13 (method #3 wall bracing system) prior to leaving the wall bracing method #3 where I then have to use R-20 batt insulation only in the wall cavity. 16% is the min.. What is the max. %?north star said:* * *rktect1,
The Method # 3 is the ' minimum ' requirements. There's nothing that says
that you cannot exceed the minimums and install additional bracing / panels.
To get your R-20 in the walls, could you use the "spray in foam" to achieve
your IECC requirement, or possibly use the R-5 rigid with the R-13 batt on
top and the insulation paper overlapped and fastened to the outside of the
studs, on the interior side?
* * *
Just answered my own question. It is in the IECC footnote h where it can't cover more than 25% of the exterior wall and if it does it requires an R-2 over the structural sheathing.rktect 1 said:It seems like I could 1/2" plywood sheath all but a 4 foot long section of a 50 foot long exterior wall, add the 1inch R-3 rigid insulation, put R-13 in the cavity and I would be able to submit a REScheck that says continuous R-5 insulation.