• Welcome to the new and improved Building Code Forum. We appreciate you being here and hope that you are getting the information that you need concerning all codes of the building trades. This is a free forum to the public due to the generosity of the Sawhorses, Corporate Supporters and Supporters who have upgraded their accounts. If you would like to have improved access to the forum please upgrade to Sawhorse by first logging in then clicking here: Upgrades

Wall cabinet above ADA toilet?

PatrickGSR94

Member
Joined
Apr 19, 2016
Messages
55
Location
Mississippi
I have a client who wants to install a wall cabinet for toiletry storage in 2-user restrooms, each one having an ADA accessible stall, and a regular stall (women's) and urinal (men's). I've seen similar cabinets in many fast-food and other restaurants, like Starbucks, etc. However I'm not sure if that would be considered a Protruding Object (which is usually "along the accessible route") or if it could be considered a shelf, etc. With a person sitting on a toilet, they're really not ever closer than 12 inches to the back wall, especially when in the seated position, or in the standing position.

What say you? I have Google searched to no end and cannot find anything definitive on the subject.
 
Depends on whether it is a tank or flushometer type toilet. Avoid head knockers when seated.
Is it for employees only? Consider reach ranges for short people.
 
Based upon A117.1 604.3.3, shelves are allowed within the clear floor space for a toilet.
1600700406240.png

The code section referred to by the OP would be 1003.3, which does not specify accessible routes, but circulation paths. The rear wall of a toilet room would not be an accessible route nor a circulation pathway.

1003.3 Protruding Objects
Protruding objects on circulation paths shall comply with the requirements of Sections 1003.3.1 through 1003.3.4.

Therefore, as ADAguy said, verify the cabinet does not protrude so far as to give someone a headache when they stand-up from the toilet.
 
Based on the cut sheets for the toilets we're using, a person would have to be straddling the bowl in order for their head to contact a cabinet above it.
 
I know we had a lengthy discussion on this previously and a little unfortunate that we don't have a "god clause" in this case(IBC)like the IRC in 2705

4. Plumbing fixtures shall be usable.
 
Based on the cut sheets for the toilets we're using, a person would have to be straddling the bowl in order for their head to contact a cabinet above it.

Picture a "tall person" sitting on the stool and leans back.
 
Last edited by a moderator:
# ~ #
" Based on the cut sheets for the toilets we're using, a person would have to be straddling the bowl in order for their head to contact a cabinet above it. "
Stranger things have happened...…..Seems like an odd place to store toiletry items......Is there any other place to store [ typical ] custodial items ?

# ~ #
 
As shelving, it is allowed per Ty J's comment on 604.3.3.
However, keep in mind that that to the extent the area around the toilet is also a "circulation path" for persons utilizing the toilet, the cabinet can't create a hazard for a blind person. There is a 4" limit for protruding objects (ADAS 307.2). The shape of toilet itself can function as a warning device below 27" high. If it is a tankless toilet, the cabinet above may pose a hazard that protrudes more than 4" beyond the toilet footprint.
 
I have a client who wants to install a wall cabinet for toiletry storage in 2-user restrooms, each one having an ADA accessible stall, and a regular stall (women's) and urinal (men's). I've seen similar cabinets in many fast-food and other restaurants, like Starbucks, etc. However I'm not sure if that would be considered a Protruding Object (which is usually "along the accessible route") or if it could be considered a shelf, etc. With a person sitting on a toilet, they're really not ever closer than 12 inches to the back wall, especially when in the seated position, or in the standing position.

What say you? I have Google searched to no end and cannot find anything definitive on the subject.

It appears that this shelf is mounted above the toilet and on the rear wall of the toilet. If this is the case, then it's not so much about protrusion but about encroachment into the toilet (water closet) clearance. There seems to be a grey area in Section 604.3.3 in the 2010 ADA Standards which states "associated grab bars,...shelves.." are permitted to overlap the water closet.

Locating shelving over the water closet might seem trivial; but, it can have a big effect on a person with a disability who is trying to utilize the fixture. The intent of Section 604.3, including 604.3.2, is that the clearance be “clear” to allow for maneuverability and transfer to the water closet from different angles. A shelf located over the water closet, even if it is located in the corner can impact maneuverability and transfer. There is a lot of guidance from the US Access Board regarding water closet clearance.

The key caveat in section 604.3.2 is the word “associated” which modifies the words that follow in the exception. In other words, the exception should be read as follows: “The required clearance around the water closet shall be permitted to overlap the water closet, associated grab bars, associated paper dispensers, associated sanitary napkin receptacles, associated coat hooks, associated shelves…”. The intent of the exception is to acknowledge that certain elements are necessary for the use of the water closet and necessary to overlap the required water closet clearance. An associated shelf would be a purse shelf, for instance. Storage shelves, however, are not associated with the use of the water closet, and thus not permitted to overlap.
 
The key caveat in section 604.3.2 is the word “associated” which modifies the words that follow in the exception. In other words, the exception should be read as follows: “The required clearance around the water closet shall be permitted to overlap the water closet, associated grab bars, associated paper dispensers, associated sanitary napkin receptacles, associated coat hooks, associated shelves…”. The intent of the exception is to acknowledge that certain elements are necessary for the use of the water closet and necessary to overlap the required water closet clearance. An associated shelf would be a purse shelf, for instance. Storage shelves, however, are not associated with the use of the water closet, and thus not permitted to overlap.
 
The key caveat in section 604.3.2 is the word “associated” which modifies the words that follow in the exception. In other words, the exception should be read as follows: “The required clearance around the water closet shall be permitted to overlap the water closet, associated grab bars, associated paper dispensers, associated sanitary napkin receptacles, associated coat hooks, associated shelves…”. The intent of the exception is to acknowledge that certain elements are necessary for the use of the water closet and necessary to overlap the required water closet clearance. An associated shelf would be a purse shelf, for instance. Storage shelves, however, are not associated with the use of the water closet, and thus not permitted to overlap.

Here's the actual wording:
1601571712500.png

I have 2 comments:
(1) You have interpreted that the word "associated" within the structure of the sentence to apply to the noun that follows it, but you stopped at "shelves". If you were being consistent, you would apply it to "accessible routes, clear floor space and clearances required at other fixtures". But no one says that clearance at a water closet can't overlap clearance at a sink. I think this points out the subjective nature of interpreting the word "associated". The adopted code language does not provide that clarity.
(2) For the sake of discussion, let's stipulate your interpretation that the shelf must be associated with the toilet. Who is to say that a shelf holding a purse is more "associated" with a water closet than a shelf storing spare toilet paper, or even a plunger? In fact, purses, coats and sanitary napkins are all things that you try to avoid putting into a water closet.
 
Could you locate a water heater in the corner of an accessible toilet room as long as all clearances are met?
 
Thank you. Could you please guide me to the correct code section?
504.1 in the 2019 California Plumbing Code which is based on the 2018 Uniform Plumbing Code. We did not adopt the plumbing code sections that are found in the International Residential Code.
 
Based upon A117.1 604.3.3, shelves are allowed within the clear floor space for a toilet.
View attachment 6981

The code section referred to by the OP would be 1003.3, which does not specify accessible routes, but circulation paths. The rear wall of a toilet room would not be an accessible route nor a circulation pathway.

1003.3 Protruding Objects
Protruding objects on circulation paths shall comply with the requirements of Sections 1003.3.1 through 1003.3.4.

Therefore, as ADAguy said, verify the cabinet does not protrude so far as to give someone a headache when they stand-up from the toilet.

A QUESTION NOT YET ASKED: "IS THE WALL CABINET REQUIRED TO BE ACCESSIBLE?"

I would answer "NO" to PatrickGSR94's question.
An accessible wall cabinet may not be located over the toilet.
 
Shelf's allowed in water closet clear area always bugged me after I saw a shelf unit sitting on the floor next to the toilet one time. I could not require it to be moved because of this code section.
 
Open or closed storage? If open what happens in a quake? if closed with a lock accessible to employees only? What of reach range compliance?
Code is still exceeded by ADA minimums. even if you claim AHJs don't enforce ADA, architects and clients must comply.
 
Open or closed storage? If open what happens in a quake? if closed with a lock accessible to employees only? What of reach range compliance?
Code is still exceeded by ADA minimums. even if you claim AHJs don't enforce ADA, architects and clients must comply.
I would not allow a cabinet over the toilet. The code is clear that shelves are allowed but not cabinets. This does not make sense to be but other sections also do not make sense to me.
 
I have a client who wants to install a wall cabinet for toiletry storage in 2-user restrooms, each one having an ADA accessible stall, and a regular stall (women's) and urinal (men's). I've seen similar cabinets in many fast-food and other restaurants, like Starbucks, etc. However I'm not sure if that would be considered a Protruding Object (which is usually "along the accessible route") or if it could be considered a shelf, etc. With a person sitting on a toilet, they're really not ever closer than 12 inches to the back wall, especially when in the seated position, or in the standing position.

What say you? I have Google searched to no end and cannot find anything definitive on the subject.
Since the use is not for the public but for (it sounds like?) janitorial storage (?), it is locked for that purpose and only if the finished bottom of the cabinet is more than 30". Figure 609.4 position of grab bars-(a) projecting objects shows projection at 12" above the the grab bar, but they don't tell you how far out the projection can go. Looks like 3". You may want to call the ADA technical assistance line to verify what they say that projection is.
 
Top