Mech
REGISTERED
2009 IBC
Type VB construction
Mixed Occupancy S-1, M, B
No sprinklers
Table 503 allows one story for S-1 and M groups and two stories for B groups.
Separated Construction (Section 508.4.3) would allow a second floor, provided it is used for Business use only
508.4.3 Allowable Height. Each separated occupancy shall comply with the building height limitations based on the type of construction of the building in accordance with Section 503.1.
Exception: Special provisions permitted by Section 509.
(see Code Commentary thread here --> http://www.thebuildingcodeforum.com/forum/commercial-building-codes/15709-2009-code-commentary-explanation-request-section-508-4-separated-occupancies.html).
508.4.4 Separation. Individual occupancies shall be separated from adjacent occupancies in accordance with Table 508.4.
Table 508.4 states "No separation requirement" between B, F-1, M, and S-1 occupancies.
Question:
Is a wall even necessary between uses to claim separated occupancies and allow a second story Business use? The proposed floor plan has an unenclosed stair leading from a first story Mercantile area up to a second story Business use. The 110+ sf landing on the second floor presents occupants with a choice of 3 rooms, each with non-fire rated doors, walls, and windows. Alternatively, second floor occupants could walk back alongside the stairs a distance of 7 feet to overlook the Mercantile area. A guardrail prevents occupants from falling off / accessing a 17 inch deep ledge that runs the width of the second floor. The required enclosed stairs is accessed through the conference room for the second floor occupants. In my over-thought assessment, the unenclosed stairs and second story landing are Business use, as they are necessary for the second story, and should need non-fire rated walls to complete the separated construction.
Thanks (especially if you made it all the way through :yawn)
Type VB construction
Mixed Occupancy S-1, M, B
No sprinklers
Table 503 allows one story for S-1 and M groups and two stories for B groups.
Separated Construction (Section 508.4.3) would allow a second floor, provided it is used for Business use only
508.4.3 Allowable Height. Each separated occupancy shall comply with the building height limitations based on the type of construction of the building in accordance with Section 503.1.
Exception: Special provisions permitted by Section 509.
(see Code Commentary thread here --> http://www.thebuildingcodeforum.com/forum/commercial-building-codes/15709-2009-code-commentary-explanation-request-section-508-4-separated-occupancies.html).
508.4.4 Separation. Individual occupancies shall be separated from adjacent occupancies in accordance with Table 508.4.
Table 508.4 states "No separation requirement" between B, F-1, M, and S-1 occupancies.
Question:
Is a wall even necessary between uses to claim separated occupancies and allow a second story Business use? The proposed floor plan has an unenclosed stair leading from a first story Mercantile area up to a second story Business use. The 110+ sf landing on the second floor presents occupants with a choice of 3 rooms, each with non-fire rated doors, walls, and windows. Alternatively, second floor occupants could walk back alongside the stairs a distance of 7 feet to overlook the Mercantile area. A guardrail prevents occupants from falling off / accessing a 17 inch deep ledge that runs the width of the second floor. The required enclosed stairs is accessed through the conference room for the second floor occupants. In my over-thought assessment, the unenclosed stairs and second story landing are Business use, as they are necessary for the second story, and should need non-fire rated walls to complete the separated construction.
Thanks (especially if you made it all the way through :yawn)