I'm looking for discussion and input from you all......On the T & P valves,
what size and type of piping are you seeing installed?
From my observations, on most [ typical 40 gal. sized ] water heaters, the
T & P valve has a 7/8" sized opening......If the opening is 7/8", can you
[ by the letter of the code - referring to Section 704.2 and / or 504.6,
Item # 3, 2006 IPC ], install 3/4" sized cpvc or 3/4" pex and be
compliant?
My contention is that if the 3/4" cpvc is installed, that the inside
diameter has indeed been reduced in the direction of flow, and
reduced in size smaller than the opening of the T & P valve.
Thoughts...
FWIW, ...as some may remember, the missing "Uncle Bob" used to be
very adamant about this requirement........Even on the use of 3/4" pex.
Thanks for your input!
* * * *