well this may be it...
“New Assembly” section of the 2012 edition of NFPA 101®, Life Safety Code®, Paragraph 12.3.4.1.1 requires that assembly occupancies with occupant loads of more than 300 and all theaters with more than one audience viewing room have an approved fire alarm system. The code also requires that occupants be notified from a constantly attended receiving station via a voice communication or a public address (PA) system, as long as it meets the following conditions: “(1) Occupant notification, either live or recorded, shall be initiated at a constantly attended receiving station by personnel trained to respond to an emergency. (2) An approved secondary power supply shall be provided for other than existing, previously approved systems. (3) The system shall be audible above the expected ambient noise level. (4) Emergency announcements shall take precedence over any other use...