Slab on grade single story home.Ground floor?
So wet location...No Bueno....Slab on grade single story home.
In the spirit of the thread title, what if the ENT is in the slab itself, and under the slab there is a vapor barrier over insulation over a capillary break (drain rock)?So wet location...No Bueno....
Not per the NEC and I agree as an experienced electrician.In the spirit of the thread title, what if the ENT is in the slab itself, and under the slab there is a vapor barrier over insulation over a capillary break (drain rock)?
Seems like that would make it a dry location. But that would be an atypical condition.
Cheers, Wayne
Oh?Not per the NEC and I agree as an experienced electrician.
When you have direct experience pulling wires out of conduit that is run under a slab but on top of the vapor barrier and then have to vacuum out all of the water so you can pull new wire, you might understand. All underground/under slab conduit fills with water, even from condensation. Direct experience in construction, specifically electrical contracting for decades teaches you that.Oh?
The definition of "Location, Wet" refers to "concrete slabs or masonry in direct contact with the earth". The implication is that a concrete slab not in direct contact with the earth would not necessarily be a wet location.
Cheers, Wayne
How often do we do things 100% right 100% of the time? Almost never I would guess.Now, to continue with your hyper-technical thought process. How do you know there is a vapor barrier in place when you get there as the electrical inspector? How do you know that 100% of the concrete slab is isolated from the earth and that no part whatsoever is touching the earth? Did you know that the vapor barrier you are referring to is for underneath the slab? Did you know that the sides of the slab are backfilled against with earth when you pull away the forms and grade the property? Did you know that in many areas, grade beams and pilings connect directly to the slab? Are you familiar with capillary action? How about during construction when it rains several times before 'dry in' is complete? Where do you think the water goes? Did you know concrete is porous?
Maybe in a hypothetical world, there is a possibility that this may not be a violation under the most perfect of conditions; however, in the real world, the one that counts, NM cable in the conduit that goes under a slab on grade, this is most definitely a violation and any qualified electrician with 1/4 of a brain knows better than to do that which is why the hypothetical question I posed is just that, hypothetical because the electrician on this job knows what he is doing and pulled THWN through the conduit.
Interesting...I'm still going to go with Jar...but....Oh?
The definition of "Location, Wet" refers to "concrete slabs or masonry in direct contact with the earth". The implication is that a concrete slab not in direct contact with the earth would not necessarily be a wet location.
Cheers, Wayne
Yeah 317 doesn't say what most of us think it does, this is the section you would have to cite for stringers I believe and it doesn't really fit that well:There was a thread a while back about a stair in a basement and I raised my concern that it was plain untreated lumber on the slab. I was corrected that the vapor barrier meant that the slab was not in contact with the ground. Not that I see that same requirement of not in contact with the ground with a different spin.
I'm familiar with this idea and I have no reason to doubt it.When you have direct experience pulling wires out of conduit that is run under a slab but on top of the vapor barrier and then have to vacuum out all of the water so you can pull new wire, you might understand. All underground/under slab conduit fills with water, even from condensation.
But it doesn't consider any basement damp. It considers "some" basements damp. Any new building with a damp basement has a serious design problem, but there certainly are plenty of such buildings in the existing stock.Lets go at it from another direction....If the NEC is considering any basement damp,
No, not every slab is damp. Concrete doesn't generate moisture. If a piece of wood in the same location wouldn't be subject to "moderate degrees of moisture", then concrete in that location won't be damp.I am considering every slab as such
Agreed that you can't run NM cable directly in the slab. But ENT is not so restricted, and inside ENT is different from being "embedded" or in a shallow chase....And I would likely argue that in the slab is embedded and/or similar to the "shallow chase" provision
Are you aware of any commercially available products that are listed as NM-C and not also listed as UF?How about NM-C?
We will agree to disagree.....But it doesn't consider any basement damp. It considers "some" basements damp. Any new building with a damp basement has a serious design problem, but there certainly are plenty of such buildings in the existing stock.
No, not every slab is damp. Concrete doesn't generate moisture. If a piece of wood in the same location wouldn't be subject to "moderate degrees of moisture", then concrete in that location won't be damp.
Agreed that you can't run NM cable directly in the slab. But ENT is not so restricted, and inside ENT is different from being "embedded" or in a shallow chase.
Cheers, Wayne
That is why they use NM-CLets go at it from another direction....If the NEC is considering any basement damp, I am considering every slab as such...And I would likely argue that in the slab is embedded and/or similar to the "shallow chase" provision
So did you run out of amo or can you keep going?When you have direct experience pulling wires out of conduit that is run under a slab but on top of the vapor barrier and then have to vacuum out all of the water so you can pull new wire, you might understand. All underground/under slab conduit fills with water, even from condensation. Direct experience in construction, specifically electrical contracting for decades teaches you that.
Now, to continue with your hyper-technical thought process. How do you know there is a vapor barrier in place when you get there as the electrical inspector? How do you know that 100% of the concrete slab is isolated from the earth and that no part whatsoever is touching the earth? Did you know that the vapor barrier you are referring to is for underneath the slab? Did you know that the sides of the slab are backfilled against with earth when you pull away the forms and grade the property? Did you know that in many areas, grade beams and pilings connect directly to the slab? Are you familiar with capillary action? How about during construction when it rains several times before 'dry in' is complete? Where do you think the water goes? Did you know concrete is porous?
Maybe in a hypothetical world, there is a possibility that this may not be a violation under the most perfect of conditions; however, in the real world, the one that counts, NM cable in the conduit that goes under a slab on grade, this is most definitely a violation and any qualified electrician with 1/4 of a brain knows better than to do that which is why the hypothetical question I posed is just that, hypothetical because the electrician on this job knows what he is doing and pulled THWN through the conduit.
If we all agree that conduit in an elevated slab is a dry location, then clearly that is also achievable for a slab on grade with the proper detailing. [Again, in the slab, not under it.]So did you run out of ammo or can you keep going?
Not out of ammo, just clarifying intent and common sense vs hypothetical extremes.So did you run out of amo or can you keep going?
The "proper" way to detail a slab on grade within the thermal envelope in cold climates (capillary break, under-slab and perimeter insulation, vapor barrier) is going to yield a dry location for conduit within it when well executed.Not out of ammo, just clarifying intent and common sense vs hypothetical extremes.