Sharlene
REGISTERED
There is no definition in the 2015 IBC for supporting construction. Is it defined as columns and beams or does it include the bar joists?
Building is type VB, sprinklered. I am trying to provide a 1 hour floor assembly to separate occupancies. In the 2015 IBC, 711.2.3 Supporting Construction. The supporting construction shall be protected to afford the required fire-resistance rating of the horizontal assembly supported. Exception: In buildings of Type IIB, IIIB, and VB construction, the construction supporting the horizontal assembly is not required to be fire-resistance rated at the following: Horizontal assemblies at the separation of dwelling units and sleeping units as required by Section 420.3. I'm trying to provide the one hour separation for the floor only without doing anything to the bar joists below.
Building is type VB, sprinklered. I am trying to provide a 1 hour floor assembly to separate occupancies. In the 2015 IBC, 711.2.3 Supporting Construction. The supporting construction shall be protected to afford the required fire-resistance rating of the horizontal assembly supported. Exception: In buildings of Type IIB, IIIB, and VB construction, the construction supporting the horizontal assembly is not required to be fire-resistance rated at the following: Horizontal assemblies at the separation of dwelling units and sleeping units as required by Section 420.3. I'm trying to provide the one hour separation for the floor only without doing anything to the bar joists below.