• Welcome to the new and improved Building Code Forum. We appreciate you being here and hope that you are getting the information that you need concerning all codes of the building trades. This is a free forum to the public due to the generosity of the Sawhorses, Corporate Supporters and Supporters who have upgraded their accounts. If you would like to have improved access to the forum please upgrade to Sawhorse by first logging in then clicking here: Upgrades

What is the difference between a "metal building" and a "metal framed building"?

ccollings

Registered User
Joined
Sep 4, 2020
Messages
103
Location
Cleveland
in the IECC table C402.2 under wall insulation there are different requirements for a "metal building" and a "metal framed building". I can't find anywhere that defines what the difference is.
 
IMHO … a metal building has structural steel columns and rafters with sheetmetal skin. A farm style building. A metal framed building could have structural steel columns with brick veneer and asphalt shingles. Or a built-up flat roof.
 
Interesting question. I would have thought metal siding makes it a metal building, whether stick (wood or steel studs ) frame or post frame. A steel framed building would be structural steel which would include the pre-engineeted style: Butler buildings, red iron buildings, etc. But I don't know. Someone call ICC?
 
IMHO … a metal building has structural steel columns and rafters with sheetmetal skin. A farm style building. A metal framed building could have structural steel columns with brick veneer and asphalt shingles. Or a built-up flat roof.
that's my interpretation as well. the project i'm doing is a pre-engineered steel frame building with metal siding which falls squarely in the metal building category no matter how you slice it.
 
This building designation and difference in required insulation doesn't make a lot of sense to me. Both appear to require cavity insulation as well as continuous insulation. That implies that there is a framing cavity in both. If a metal building is a structural steel superstructure, like a PEMB, with structural steel columns, girts, beams, etc., are they not often constructed without traditional framing cavities? Does the energy code now disallow that? If a metal framed building is a building with all light gauge, cold formed, repetitive members without a structural steel superstructure, it naturally has the cavities. If both have cavities and cavity insulation (of the same R-value), why the difference in the continuous insulation value?

The descriptions I offer and it seems others as well make sense to me, but they really should be defined, maybe that would help eliminate my confusion. I may have the opportunity to ask some of the energy guru's this week, I'll report if I gain any useful knowledge.
 
IMHO
Metal Framed = Steel stud construction
Metal Building = metal columns Purlins and Girders
This is correct. Metal framed = framed walls using metal studs (not wood framed, wood studs).

iphone-backup2-22-010.jpg


Metal building is short for "pre-engineered metal building" which is a system of rigid steel frames, with horizontal wall girts (purlins at the roof) spanning between the frames, usually 20-25 foot spans, spaced every 3 to 5 feet vertically. Then vertical metal siding on the outside, and sometimes with vinyl-faced fiberglass insulation sandwiched in between the girts/purlins and the outer metal skin.

Pre%20Engineered%20Metal%20Building.jpeg


The cavity vs. continuous insulation has to do with the thermal bridging. With both types of construction, there's thermal bridging happening at each vertical metal stud, or at each horizontal metal girt/purlin. The addition of continuous insulation outside the framing helps to reduce or eliminate the thermal briding effect.
 
This is correct. Metal framed = framed walls using metal studs (not wood framed, wood studs).

iphone-backup2-22-010.jpg


Metal building is short for "pre-engineered metal building" which is a system of rigid steel frames, with horizontal wall girts (purlins at the roof) spanning between the frames, usually 20-25 foot spans, spaced every 3 to 5 feet vertically. Then vertical metal siding on the outside, and sometimes with vinyl-faced fiberglass insulation sandwiched in between the girts/purlins and the outer metal skin.

Pre%20Engineered%20Metal%20Building.jpeg


The cavity vs. continuous insulation has to do with the thermal bridging. With both types of construction, there's thermal bridging happening at each vertical metal stud, or at each horizontal metal girt/purlin. The addition of continuous insulation outside the framing helps to reduce or eliminate the thermal briding effect.
Agree. I've worked with many PEMB projects. Up "north" it's not too unusual to have both. I'm used to seeing a pre-manufactured insulated panel as the exterior skin - providing the continuous rigid insulation. This in addition to the interior insulation.
 