For the sake of the conversation, when I open my code book, this is what I read. Is it the same for y'all, or is yours modified?
1004.2 Cumulative occupant loads. Where the path of
egress travel includes intervening rooms, areas or spaces,
cumulative occupant loads shall be determined in accordance
with this section.
1004.2.1 Intervening spaces or accessory areas. Where
occupants egress from one or more rooms, areas or spaces
through others, the design occupant load shall be the
combined occupant load of interconnected accessory or
intervening spaces. Design of egress path capacity shall be
based on the cumulative portion of occupant loads of all
rooms, areas or spaces to that point along the path of
egress travel.
1004.2.2 Adjacent levels for mezzanines. That portion of
the occupant load of a mezzanine with required egress
through a room, area or space on an adjacent level shall be
added to the occupant load of that room, area or space.
1004.2.3 Adjacent stories. Other than for the egress
components designed for convergence in accordance with
Section 1005.6, the occupant load from separate stories
shall not be added.
1004.3 Multiple function occupant load. Where an area
under consideration contains multiple functions having
different occupant load factors, the design occupant load for
such area shall be based on the floor area of each function
calculated independently.
1004.4 Multiple occupancies. Where a building contains
two or more occupancies, the means of egress requirements
shall apply to each portion of the building based on the occupancy
of that space. Where two or more occupancies utilize
portions of the same means of egress system, those egress
components shall meet the more stringent requirements of all
occupancies that are served.