• Welcome to the new and improved Building Code Forum. We appreciate you being here and hope that you are getting the information that you need concerning all codes of the building trades. This is a free forum to the public due to the generosity of the Sawhorses, Corporate Supporters and Supporters who have upgraded their accounts. If you would like to have improved access to the forum please upgrade to Sawhorse by first logging in then clicking here: Upgrades

When a wire is too large for the lug and you find this.......

Why is a bond bushing required? Don't know the full scope of what we are looking at by the closeup pic?
It is a service enclosure with a metal raceway through an intact KO. The picture is not clear but one of the knockouts is left in place.

250.92(B)
Method of Bonding at the Service. Bonding jumpers meeting the requirements of this article shall be used around impaired connections, such as reducing washers or oversized, concentric, or eccentric knockouts. Standard locknuts or bushings shall not be the only means for the bonding required by this section but shall be permitted to be installed to make a mechanical connection of the raceway(s).
 
Last edited:
Third picture in post #24

Isn't that a bonding screw that's bent and not being used? and a regular lock nut on the other?
 
The bonding screw is purposely bent like that on the bonding lock-nut, correct?
 