1) There are differences in how the codes apply but there is no differences in the electrical principles.
2) Always and would be sized according to these sections.
230.23 Size and Rating and 230.31 Size and Rating.
© Grounded Conductors. The grounded conductor shall
not be less than the minimum size as required by
250.24©.
250.24©.
(1) Sizing for a Single Raceway. The grounded conductor
shall not be smaller than the required grounding electrode
conductor specified in Table 250.66 but shall not be required
to be larger than the largest ungrounded serviceentrance
conductor(s). In addition, for sets of ungrounded
service-entrance conductors larger than 1100 kcmil copper
or 1750 kcmil aluminum, the grounded conductor shall not
be smaller than 121⁄2 percent of the circular mil area of the
largest set of service-entrance ungrounded conductor(s).
230.42 Minimum Size and Rating.
(A) General. The ampacity of the service-entrance conductors
before the application of any adjustment or correction
factors shall not be less than either 230.42(A)(1) or
(A)(2). Loads shall be determined in accordance with Part
III, IV, or V of Article 220, as applicable. Ampacity shall be
determined from 310.15. The maximum allowable current
of busways shall be that value for which the busway has
been listed or labeled.
(1) The sum of the noncontinuous loads plus 125 percent
of continuous loads