Where are ship ladders allowable by code 2009 IBC
joetheinspector
1009.11 Ship Ladders: States when ship ladders can be used: As a component of a means of egress in Group I-3 and access to unoccupied roofs
Where else is it allowable by code to use a ship ladder?
joetheinspector, I'm pretty sure that's it. Below are the 2009 and 2012 provisions from the unadulterated IBC.
2009 IBC: 1009.11 Ship ladders. Ship ladders are permitted to be used in Group I-3 as a component of a means of egress to and from control rooms or elevated facility observation stations not more than 250 square feet (23 m2) with not more than three occupants and for access to unoccupied roofs.
Ship ladders shall have a minimum tread depth of 5 inches (127 mm). The tread shall be projected such that the total of the tread depth plus the nosing projection is no less than 81/2 inches (216 mm). The maximum riser height shall be 91/2 inches (241 mm).
Handrails shall be provided on both sides of ship ladders. The minimum clear width at and below the handrails shall be 20 inches (508 mm).
2012 IBC: 1009.14 Ship ladders.
Railroad loading doors ??
Some equipment access ?
Some roof access?
Swimming pools
Ships
From the `12 IBC, Section 1015.3 - Boiler, incinerator and furnace rooms: "Two exit access doorways
are required in boiler, incinerator and furnace rooms where the area is over 500 square feet (46 m2) and
any fuel-fired equipment exceeds 400,000 British thermal units (Btu) (422 000 KJ) input capacity.
Where two exit access doorways are required, one is permitted to be a fixed ladder, or an alternating
tread device..................Exit access doorways shall be separated by a horizontal distance equal to one-half
the length of the maximum overall diagonal dimension of the room."
IMO, ...this section appears to indicate that the "fixed ladder" could indeed be a Ship's [ type ] Ladder.
from 03
1014.6.1 Gallery, grid iron and cat walk means of egress.
The means of egress from lighting and access catwalks, galleries and grid irons shall meet the requirements for occupancies in Group F-2.
1. A minimum width of 22 inches (559 mm) is permitted for lighting and access catwalks.
2. Spiral stairs are permitted in the means of egress.
3. Stair ways required by this sub section need not be
enclosed.
4. Stair ways with a minimum width of 22 inches (559mm), ladders, or spiral stairs are permitted in the
means of egress.
5. A second means of egress is not required from these
areas where a means of escape to a floor or to a roof
is provided. Ladders, alternating tread devices or
spiral stairs are permitted in the means of escape.
6. Ladders are permitted in the means of egress.