From the `12 IBC, Section 1015.3 - Boiler, incinerator and furnace rooms: "Two exit access doorways
are required in boiler, incinerator and furnace rooms where the area is over 500 square feet (46 m2) and
any fuel-fired equipment exceeds 400,000 British thermal units (Btu) (422 000 KJ) input capacity.
Where two exit access doorways are required, one is permitted to be a fixed ladder, or an alternating
tread device..................Exit access doorways shall be separated by a horizontal distance equal to one-half
the length of the maximum overall diagonal dimension of the room."
IMO, ...this section appears to indicate that the "fixed ladder" could indeed be a Ship's [ type ] Ladder.
~ & ~