Hi,
I have a project with an existing house being used in conjunction with a ballroom. The intent of the house is to hold receptions and on the second floor provide lodging for up to 9 people. They would like to be able to fit 250-299 people in the house for functions.
I was planning to submit the project as mixed use A-3 and R-3 with no separation as allowed in IEBC with a NFPA 13 sprinkler system. Unbeknownst to me, the contractor went ahead and installed a 13D system. I do not believe a 13D can be used for mixed use. However, they will be under 300 occupants, well under 12,000 SF, and no assembly spaces on other floors other than level of exit discharge. If they don't trigger the need for a sprinkler system with the A-3 occupancy, would they be able to use the 13D system as mixed use? With a straight R-3 occupancy I can only get up to 160 occupants.
Per 2012 International Existing Building Code
1011.1.1.1 Change of occupancy classification without separation.
Where a portion of an existing building is changed to a new occupancy classification or where there is a change of occupancy within a space where there is a different fire protection system threshold requirement in Chapter 9 of the International Building Code, and that portion is not separated from the remainder of the building with fire barriers having a fire-resistance rating as required in the International Building Code for the separate occupancy, the entire building shall comply with all of the requirements of Chapter 9 of this code applied throughout the building for the most restrictive occupancy classification in the building and with the requirements of this chapter.
I have a project with an existing house being used in conjunction with a ballroom. The intent of the house is to hold receptions and on the second floor provide lodging for up to 9 people. They would like to be able to fit 250-299 people in the house for functions.
I was planning to submit the project as mixed use A-3 and R-3 with no separation as allowed in IEBC with a NFPA 13 sprinkler system. Unbeknownst to me, the contractor went ahead and installed a 13D system. I do not believe a 13D can be used for mixed use. However, they will be under 300 occupants, well under 12,000 SF, and no assembly spaces on other floors other than level of exit discharge. If they don't trigger the need for a sprinkler system with the A-3 occupancy, would they be able to use the 13D system as mixed use? With a straight R-3 occupancy I can only get up to 160 occupants.
Per 2012 International Existing Building Code
1011.1.1.1 Change of occupancy classification without separation.
Where a portion of an existing building is changed to a new occupancy classification or where there is a change of occupancy within a space where there is a different fire protection system threshold requirement in Chapter 9 of the International Building Code, and that portion is not separated from the remainder of the building with fire barriers having a fire-resistance rating as required in the International Building Code for the separate occupancy, the entire building shall comply with all of the requirements of Chapter 9 of this code applied throughout the building for the most restrictive occupancy classification in the building and with the requirements of this chapter.