Your general building contractor license means that you can pull a permit to install a water heater but I think the theory is that you have an actual plumber do the work. You put an 18" high stand under it because it's in a laundry room and didn't install an emergency drain pan. You reused a 50 year old gas shut off valve that has no handle. You flattened the flexible water line, didn't secure the vent connector to the draft hood because, well there was no draft hood, and the total length of the vent is 3.5 feet. You put it in a room that is 60 sq. ft., blocked off by doors and has no combustion air openings.
All of these mistakes are understandable. By that I mean that you not being a plumber is excuse enough for making these mistakes. Well now comes the mistake shown in the picture. You installed a valve that can't close because the handle hits the water heater.
Odds are pretty good that you will call and ask me if you can shorten the handle. Oh Hell No! Remove the 18" stand when you install the smitty pan and then the water heater will clear the valve and the vent length will be back to 5'. If I must teach you how to do this you will do a fine job of it. That means that if you don't call and ask about shortening the handle, then shorten the handle, it's not too late to do the work over, it never is.
A few salient facts. The contractor pulled a permit for a re-roof. He didn't know that there would be a reason for me to meet the owner and go inside to verify detectors. I did that and as I was leaving, the owner asked me if I wanted to see the water heater or the receptacles. Shirley I do, said I. I Shirley want you to, said he. And yes we have no permits.
The contractor walked on as I was leaving. I gave him the notice and he scanned tit. His only comment was "Permits? Are you sure?" I had my chance when he flagged me down to tell me that he installed GFCI receptacles. I told him to Google tamper resistant.
All of these mistakes are understandable. By that I mean that you not being a plumber is excuse enough for making these mistakes. Well now comes the mistake shown in the picture. You installed a valve that can't close because the handle hits the water heater.
Odds are pretty good that you will call and ask me if you can shorten the handle. Oh Hell No! Remove the 18" stand when you install the smitty pan and then the water heater will clear the valve and the vent length will be back to 5'. If I must teach you how to do this you will do a fine job of it. That means that if you don't call and ask about shortening the handle, then shorten the handle, it's not too late to do the work over, it never is.
A few salient facts. The contractor pulled a permit for a re-roof. He didn't know that there would be a reason for me to meet the owner and go inside to verify detectors. I did that and as I was leaving, the owner asked me if I wanted to see the water heater or the receptacles. Shirley I do, said I. I Shirley want you to, said he. And yes we have no permits.
The contractor walked on as I was leaving. I gave him the notice and he scanned tit. His only comment was "Permits? Are you sure?" I had my chance when he flagged me down to tell me that he installed GFCI receptacles. I told him to Google tamper resistant.

Last edited by a moderator: