• Welcome to the new and improved Building Code Forum. We appreciate you being here and hope that you are getting the information that you need concerning all codes of the building trades. This is a free forum to the public due to the generosity of the Sawhorses, Corporate Supporters and Supporters who have upgraded their accounts. If you would like to have improved access to the forum please upgrade to Sawhorse by first logging in then clicking here: Upgrades

Why you bring a hammer to a CMU inspection

jar546

Forum Coordinator
Joined
Oct 16, 2009
Messages
11,075
Location
Somewhere Too Hot & Humid
This was suppose to be poured solid but was not. This is why you bring a hammer to an inspection. This is a critical attachment point for the door, and a bond beam. In another section they completely missed a 10' fill cell pour for a wall being used as a sheer wall. Trust no one.

IMG_2993.JPG
 
I can only imagine the trouble that I would be in if I punched holes in CMU.

I was a carpenter working for an alcoholic superintendent. We were remodeling a Payless drug store. There was a mostly glass wall between the garden dept. and the store. It came time to demo the wall. The drunk took a 20 oz. hammer and threw it at an 8’ x 8’ glass pane. The hammer ricocheted off the glass, shot into the camera dept. and smashed a boom box.

The stores were identical. I was the superintendent on the next store. I saved the glass from that store and a few more. The plan was to enclose my swimming pool. I never got around to it and the glass was used for a greenhouse instead. I made a rack to haul the glass from the lumber that was used to build a security catwalk. The catwalk was made from scaffold plank material.
 
Not trying to downplay the omission of grout, but I don't understand several things that led to "hammer time":

1. Does your jurisdiction require deputy inspections during grouting?
2. Did it appear solid grouted when looking down from above, such that only smashing the block would reveal the void? Or was the void also visible from above?
3. Hammering the block seems like a destructive testing / last resort for verification. Were there other clues that first led you to be suspicious the cels weren't grouted? Or is this standard practice for grout inspection? (Not trying to be critical, but trying to understand here.)

1695170192996.png
 
1) I don't know what deputy inspections means.
2) I don't know, I arrived after the fact.
3) If it was grouted as required by the plans, it would not be destructive. This is standard practice to make sure they did not block the cells to save concrete.

Apparently the inspection paid off. Normally the bottom block are chipped out, inspected for rebar, then covered with plywood and then removed after the concrete is poured. Normally you don't find this stuff unless inspection holes are missing or were missed during the pre-fill cell inspection.
 
Not trying to downplay the omission of grout, but I don't understand several things that led to "hammer time":

1. Does your jurisdiction require deputy inspections during grouting?
2. Did it appear solid grouted when looking down from above, such that only smashing the block would reveal the void? Or was the void also visible from above?
3. Hammering the block seems like a destructive testing / last resort for verification. Were there other clues that first led you to be suspicious the cels weren't grouted? Or is this standard practice for grout inspection? (Not trying to be critical, but trying to understand here.)
Here are some examples. I've posted pics like this before. Click on the pics to enlarge.

IMG_2813.JPGIMG_2815.JPGIMG_2868.JPG
 
CMU construction is common in Florida and not so much in So. California. So it makes sense that you have stringent inspection techniques. Tapping the face shell with a hammer might tell you if the cell has grout. We have a special inspectors performing inspections during masonry construction. It might be periodic inspections.
 
1) I don't know what deputy inspections means.
2) I don't know, I arrived after the fact.
3) If it was grouted as required by the plans, it would not be destructive. This is standard practice to make sure they did not block the cells to save concrete.

Apparently the inspection paid off. Normally the bottom block are chipped out, inspected for rebar, then covered with plywood and then removed after the concrete is poured. Normally you don't find this stuff unless inspection holes are missing or were missed during the pre-fill cell inspection.

OK, so on this kind of project, the CMU is not the finish surface of the wall; it will get covered with some other finish in the future; thus, hitting it with a hammer for purposes of inspection has no detrimental effect on the finish surface of the wall.

Is this correct?
 
OK, so on this kind of project, the CMU is not the finish surface of the wall; it will get covered with some other finish in the future; thus, hitting it with a hammer for purposes of inspection has no detrimental effect on the finish surface of the wall.

Is this correct?
Pounding on the wall with a hammer is apparently an accepted practice in Jeff's jurisdiction. If that were done anywhere that I have worked, there would be a valid complaint. If I had a reason to suspect that the cells were not filled, I would resort to a 1/4" drill bit and even that would raise eyebrows.
 
You do not have to hit the block hard enough to knock a hole in the CMU to determine if it is hollow or not, just tapping on it you can tell if it is solid filled cell or not. 15 years of knocking holes in new and existing CMU walls in South Florida, it's not rocket science.
 
Pounding on the wall with a hammer is apparently an accepted practice in Jeff's jurisdiction. If that were done anywhere that I have worked, there would be a valid complaint. If I had a reason to suspect that the cells were not filled, I would resort to a 1/4" drill bit and even that would raise eyebrows.

Again, out here in California it would be straightforward, as our structural plans for CMU would include at least these 3 notes (along with others) for grouting:

1695245049044.png

If a contractor claimed to have grouted walls without the required deputy inspection, as a default they would theoretically have to tear it out and start over. This of course would freak them out, and they would seek to pay for other methods of grout verification in lieu of demolition, including any/all of the following:
  1. Non-intrusive:
    1. X-ray
    2. Ultrasound
    3. Pachometer
  2. Intrusive:
    1. Random core samples
    2. Hammer time
But a city inspector would not pre-emptively chip open a wall (coring, hammer, whatever) or do other intrusive work without first reviewing the other "pick your poison" alternatives with the contractor.


Note that even if a hammer revealed the presence of grout, without core samples tests for design strength the structural engineer might not grant final signoff.
 

Attachments

  • 1695245015327.png
    1695245015327.png
    20.7 KB · Views: 3
IBC 2021, Chapter 17, Special Inspections:

1705.4 Masonry construction. Special inspections and tests
of masonry construction shall be performed in accordance
with the quality assurance program requirements of TMS
402 and TMS 602.
Exception: Special inspections and tests shall not be
required for:
1. Empirically designed masonry, glass unit
masonry
or masonry veneer designed in accordance
with Section 2109, Section 2110 or Chapter
14, respectively, where they are part of a structure
classified as Risk Category I, II or III.
2. Masonry foundation walls constructed in accordance
with Table 1807.1.6.3(1), 1807.1.6.3(2),
1807.1.6.3(3) or 1807.1.6.3(4).
3. Masonry fireplaces, masonry heaters or masonry
chimneys installed or constructed in accordance
with Section 2111, 2112 or 2113, respectively.
 