Sifu
SAWHORSE
- Joined
- Sep 3, 2011
- Messages
- 3,318
IRC 2006, 613.2 Window sills. Requires guards on windows >72" above grade & <24" AFF which prevent opening >4".
IRC 2006, 310.1 Emergency escape openings. Requires minimum clear openings without keys, tools or special knowledge.
If a compliant EE opening is located >72" above grade and < 24" AFF and is the only window in a bedroom can these codes both be complied with?
The code permits an ASTM F 2006 or 2090 device by exception, maybe those devices address the concern. Anybody seen those listings? The devices I have seen require an extra motion and special knowledge but maybe they are not the listed devices.
The code does not apply to fixed windows, had a builder try to screw a window shut. I said not permitted (not an EE opening) but now am wondering why. No different than a builder putting up a handrail then taking it down after I leave, right?
Got a house full of casements set lower than 24" AFF. Wondering what device would be installed on them.
IRC 2006, 310.1 Emergency escape openings. Requires minimum clear openings without keys, tools or special knowledge.
If a compliant EE opening is located >72" above grade and < 24" AFF and is the only window in a bedroom can these codes both be complied with?
The code permits an ASTM F 2006 or 2090 device by exception, maybe those devices address the concern. Anybody seen those listings? The devices I have seen require an extra motion and special knowledge but maybe they are not the listed devices.
The code does not apply to fixed windows, had a builder try to screw a window shut. I said not permitted (not an EE opening) but now am wondering why. No different than a builder putting up a handrail then taking it down after I leave, right?
Got a house full of casements set lower than 24" AFF. Wondering what device would be installed on them.