Does the code allow wood furring strips to be used on a ceiling in Type I or II construction to fur out for drywall?
Your premier resource for building code knowledge.
This forum remains free to the public thanks to the generous support of our Sawhorse Members and Corporate Sponsors. Their contributions help keep this community thriving and accessible.
Want enhanced access to expert discussions and exclusive features? Learn more about the benefits here.
Ready to upgrade? Log in and upgrade now.
See IBC Section 603.1 #18 which references to Section 803.13
803.13 Application of Interior Finish Materials to Fire-Resistance-Rated or Noncombustible Building Elements
Where interior finish materials are applied on walls, ceilings or structural elements required to have a fire-resistance rating or to be of noncombustible construction, these finish materials shall comply with the provisions of this section.
803.13.1 Direct Attachment and Furred Construction
Where walls and ceilings are required by any provision in this code to be of fire-resistance-rated or noncombustible construction, the interior finish material shall be applied directly against such construction or to furring strips not exceeding 1 3/4 inches (44 mm), applied directly against such surfaces.
803.13.1.1 Furred Construction
If the interior finish material is applied to furring strips, the intervening spaces between such furring strips shall comply with one of the following:
- Be filled with material that is inorganic or noncombustible;
- Be filled with material that meets the requirements of a Class A material in accordance with Section 803.1.1 or 803.1.2; or
- Be fireblocked at a maximum of 8 feet (2438 mm) in every direction in accordance with Section 718.
Because you don't have to. Wood is allowed.why not use metal hat channels?
Wood, yes, with conditionsBecause you don't have to. Wood is allowed.
I'd agree that hat channel is probably the "better" method; however, if the code allows it, can/should you reject it?
Same requirements, just different materials.How are wood and metal strips treated differently? Seems like both need to meet the 3 requirements:
- Be filled with material that is inorganic or noncombustible;
- Be filled with material that meets the requirements of a Class A material in accordance with Section 803.1.1 or 803.1.2; or
- Be fireblocked at a maximum of 8 feet (2438 mm) in every direction in accordance with Section 718.
Ok. In #3 Tim says why not use metal hat channels, with the implication it would make a difference in codevapplication.Same requirements, just different materials.
Yeah, I thought the same... but per my reading of 803.13.1.1, there is no differentiation, thus the same implications whether wood or hat channel.Ok. In #3 Tim says why not use metal hat channels, with the implication it would make a difference in codevapplication.
Yeah, I thought the same... but per my reading of 803.13.1.1, there is no differentiation, thus the same implications whether wood or hat channel.
803.13.1.1 Furred Construction
If the interior finish material is applied to furring strips, the intervening spaces between such furring strips shall comply with one of the following:
- Be filled with material that is inorganic or noncombustible;
- Be filled with material that meets the requirements of a Class A material in accordance with Section 803.1.1 or 803.1.2; or
- Be fireblocked at a maximum of 8 feet (2438 mm) in every direction in accordance with Section 718.
7/8” metal hat channel isn’t framing, it’s for furring out a wallIsn't hat channel, hat channel and wood furring strips are 'furring' strips? The section is for furring strips, not metal framing.