We have detailed a ceiling with wood to create a light cove.
Our argument to do this was first based on the fact that this is blocking. The building department and us could not come to the same conclusion of the definition of blocking and they felt this was not blocking.
Therefore we proposed the following code section and argument:
Thanks.
Our argument to do this was first based on the fact that this is blocking. The building department and us could not come to the same conclusion of the definition of blocking and they felt this was not blocking.
Therefore we proposed the following code section and argument:
- Section 603 – Combustible Material in Type I & Type II Construction:
- Exception 18; Nailing or furring strips as permitted by Section 803.11/803.11.1
This exception allows combustible nailing and furring for interior finishes. Within these sections it states; the interior finish material shall be applied directly against such construction or to furring strips not exceeding 1 3/4 inches. This would be a compatible code section where there is a finish shown attached to a nailer which is of compliant thickness.
Thanks.