raider1
Silver Member
I will also add that the shock hazard for a 240 volt A/C disconnect is greater than that of the 120 volt receptacle for the garbage disposer.
Chris
Chris
NEC 90.1(A): "The purpose of this Code is the practical safeguarding of persons and property from hazards arising from the use of electricity." I believe that it is sometimes necessary to examine the A/C disconnect for voltage while it is energized. IMO 110.26(A) applies. I also think it is sometimes necessary to test three way light switches while energized to see why they are not working correctly. 110.26(A) is very broadly written and it is hard to know where to decide to draw the line on it's application. There have been unsuccessful attempts to come up with changes to it's text to make it less ambiguous. At the present, it is left up to the AHJ to decide how to apply it. The best way for me to get a handle on it is to look back at that opening statement in article 90. Is it practical to provide working space in front of every receptacle and light switch? I don't think so. Is it practical to provide working space in front of the A/C disconnect? I think so.gbhammer said:So you’re saying that if there are conditions that would make it impractical to have working space clearance for an AC disconnect; then it’s ok to ignore the rule.
(A) Working Space. Working space for equipment operating at 600 volts, nominal, or less to ground and likely to require examination, adjustment, servicing, or maintenance while energized shall comply with the dimensions of 110.26(A)(1), (A)(2), and (A)(3) or as required or permitted elsewhere in this Code.Key to understanding 110.26 is the division of requirements for spaces about electrical equipment in two separate and distinct categories: working space and dedicated equipment space. The term working space generally applies to the protection of the worker, and dedicated equipment space applies to the space reserved for future access to electrical equipment and to protection of the equipment from intrusion by nonelectrical equipment. The performance requirements for all spaces about electrical equipment are set forth in this section. Storage of material that blocks access or prevents safe work practices must be avoided at all times.
2008 NEC HANDBOOKThe intent of 110.26(A) is to provide enough space for personnel to perform any of the operations listed without jeopardizing worker safety. These operations include examination, adjustment, servicing, and maintenance of equipment. Examples of such equipment include panelboards, switches, circuit breakers, controllers, and controls on heating and air-conditioning equipment. It is important to understand that the word examination, as used in 110.26(A), includes such tasks as checking for the presence of voltage using a portable voltmeter.Minimum working clearances are not required if the equipment is such that it is not likely to require examination, adjustment, servicing, or maintenance while energized. However, “sufficient” access and working space are still required by the opening paragraph of 110.26.
Yes it does,mtlogcabin said:Does the NEC have a definition of "equipment"
deleted. Chris got it first.mtlogcabin said:Does the NEC have a definition of "equipment"
It does not say all electrical equipment.gbhammer said:Like ICE, I do not take issue with any of what you are all saying. What I have a problem with is the fact that if you read the code as it is written, then we could never build a building with out some form of noncompliance ("all electric equipment" leaves no room for discusion).
ICE said:Oh and Mr. Kennedy, look at what you started.
I just figured it would be in my best interests to say out of it at this point.ICE said:Well nobody has said anything for some time now, so I guess we are all in agreement. I like happy endings.
With all due respect this is not a good justification for allowing one and not the other as plenty of people have bought the ranch from being shocked by either of those voltages. A commercial fisherman friend of mine used to always say that the higher AC voltages were safer as they would "push you off while the 110 would have a tendency to make you stick". Regarding the question what ICE says makes sense but I wouldn't be surprised to have the correction written up to move the disconnect.raider1 said:I will also add that the shock hazard for a 240 volt A/C disconnect is greater than that of the 120 volt receptacle for the garbage disposer.Chris
I already know your position and I respect your opinion.chris kennedy said:I just figured it would be in my best interests to say out of it at this point.
My point exactly about 'all', and what everyone seems to ignore, which is something that ICE brought up; you can make the examination elsewhere. 110.26 say’s the working space is for when you need ready and safe operation and maintenance. The word "ready" would imply that it is only for equipment that requires a quick fix or needs continued maintenance/work.ICE said:No code based argument is presented against my position other than 110.26, implying that the use of a voltage tester constitutes "examination." That premise places any and all electrical equipment within the parameters of 110.26. 110.26 would then require receptacles, switches, fixtures, outlets and any other point that a tester might be applied, to have working space. Obviously, that can't be the case.Dead receptacle. What do you do? Test with a meter. Confirmed dead. What's next? Remove cover plate and receptacle, test conductors. What just happened? Was a receptacle examined while energized? Was the conductor examined while energized? All of it is electrical equipment per the definition. All of it is likely to be examined while energized if the use of a tester constitutes examination.
HVAC equipment has been arbitrarily elevated above equipment such a receptacles, garbage disposals, etc. What about the furnace? Nobody will claim that the disconnect for a furnace shall have working space provided. Why is that? How does a condenser stand out from any other equipment? Were it the intent of the code that the lone disconnect to require working space is the disconnect provided for a condenser, the code would say exactly that.
And finally, working space is a restriction placed on owners that takes space away from the owner. All electrical equipment is hazardous and working space is reserved for equipment that presents a heightened hazard.
Tiger