I can add the wording provided that someone doesn't get mad at me.Builder Bob said:It is a shame that wording can't be added,since these code section do not correlate to the 2006 IRC..
Here is 250.64(B) again this is the 2011 wording.250.53 Grounding Electrode System Installation.Informational Note: See 547.9 and 547.10 for special
grounding and bonding requirements for agricultural
buildings.
(A) Rod, Pipe, and Plate Electrodes. Rod, pipe, and plate
electrodes shall meet the requirements of 250.53(A)(1)
through (A)(3).
(1) Below Permanent Moisture Level. If practicable, rod,
pipe, and plate electrodes shall be embedded below permanent
moisture level. Rod, pipe, and plate electrodes shall be
free from nonconductive coatings such as paint or enamel.
(2) Supplemental Electrode Required. A single rod, pipe,
or plate electrode shall be supplemented by an additional
electrode of a type specified in 250.52(A)(2) through
(A)(8). The supplemental electrode shall be permitted to be
bonded to one of the following:
(1) Rod, pipe, or plate electrode
(2) Grounding electrode conductor
(3) Grounded service-entrance conductor
(4) Nonflexible grounded service raceway
(5) Any grounded service enclosure
Exception: If a single rod, pipe, or plate grounding electrode
has a resistance to earth of 25 ohms or less, the
supplemental electrode shall not be required.
(3) Supplemental Electrode. If multiple rod, pipe, or plate
electrodes are installed to meet the requirements of this
section, they shall not be less than 1.8 m (6 ft) apart.
Chris(B) Securing and Protection Against Physical Damage.Where exposed, a grounding electrode conductor or its enclosure
shall be securely fastened to the surface on which it
is carried. Grounding electrode conductors shall be permitted
to be installed on or through framing members. A 4
AWG or larger copper or aluminum grounding electrode
conductor shall be protected if exposed to physical damage.
A 6 AWG grounding electrode conductor that is free from
exposure to physical damage shall be permitted to be run
along the surface of the building construction without metal
covering or protection if it is securely fastened to the construction;
otherwise, it shall be protected in rigid metal
conduit (RMC), intermediate metal conduit (IMC), rigid
polyvinyl chloride conduit (PVC), reinforced thermosetting
resin conduit (RTRC), electrical metallic tubing (EMT), or
cable armor. Grounding electrode conductors smaller than 6
AWG shall be protected in RMC, IMC, PVC, RTRC, EMT,
or cable armor.
dcspector said:Oh gee Thanks for letting us all know what the section numbers actually read that I posted. We know what the code reads Mr Mule/ Moderator. Yes they do pertain to this install per the picture I have and can see.
Also Appendix Q of the 2006 IRC has cross references.Builder Bob said:It is a shame that wording can't be added,since these code section do not correlate to the 2006 IRC..
If there are, they are probably buried in the planter. Good pickup even in the electrical section!north star said:<<< I cannot determine if there are any weep holes in the brick veneer or not.
Possibly R703.7.6 - `06 IRC.
>>>
Mule said:Would you like for me to add the wording on mine? I'll add the wording if you want me too... I really don't mind...it's just that...From another thread..
LOL, I remember that, 2 weeks ago Sunday? Greg had his knickers in a twist that morning!:lol::lol::lol:dcspector said:Oh gee Thanks for letting us all know what the section numbers actually read that I posted. We know what the code reads Mr Mule/ Moderator. Yes they do pertain to this install per the picture I have and can see.