Forum Coordinator
http://www.interlockkit.com/
There are a lot of generators out there.
Sent from my iPad using Tapatalk HD
Without looking at the UL White Book I say yes.jwelectric said:Look at FTCN of the UL White Book and then answer
FTCN.GuideInfo - Engine Generators for Portable UseRider Rick said:Without looking at the UL White Book I say yes. Why not?
A direct conflict with the NEC definition of SDS wouldn't you say Mike?jwelectric said:1. The generator is considered a separately derived system in accordance with ANSI/NFPA 70, "National Electrical Code" (NEC).
No Sir I don't believe that there is a conflict at all with the NEC. I believe that the NEC is clear that a self contained generator set is a SDS And must be connected with a transfer switch that switches the neutral.chris kennedy said:A direct conflict with the NEC definition of SDS wouldn't you say Mike?
Could you reference the art that states this please?jwelectric said:I believe that the NEC is clear that a self contained generator set is a SDS And must be connected with a transfer switch that switches the neutral.
By UL's Listing of the stand alone generators and 250.34 of the NEC250.34 Portable and Vehicle-Mounted Generators.chris kennedy said:Could you reference the art that states this please?
And what does the Informational Note 1 under 250.30 in the 2011 say?jwelectric said:Pay close attention to the Informational Note included in this section.
250.30 addresses a SDS.
Yes I know that the Note is not enforceable but the section referenced is very much enforceable
Just fail to see how you can make the above statement.jwelectric said:I believe that the NEC is clear that a self contained generator set is a SDS And must be connected with a transfer switch that switches the neutral.
Informational Note No. 1: An alternate ac power source, such as an on-site generator, is not a separately derived system if the grounded conductor is solidly interconnected to a service-supplied system grounded conductor. An example of such a situation is where alternate source transfer equipment does not include a switching action in the grounded conductor and allows it to remain solidly connected to the service-supplied grounded conductor when the alternate source is operational and supplying the load served.But I think we are talking about generators outlined in 250.34 are we not? This section says nothing about a portable generator.chris kennedy said:And what does the Informational Note 1 under 250.30 in the 2011 say?
Just repeating what I have been told at these IAIE meeting I attendchris kennedy said:Just fail to see how you can make the above statement.
(B) Nonseparately Derived System. If the generator is installed as a nonseparately derived system, and overcurrent protection is not integral with the generator assembly, a supply-side bonding jumper shall be installed between the generator equipment grounding terminal and the equipment grounding terminal, bar, or bus of the disconnecting mean(s). It shall be sized in accordance with 250.102© based on the size of the conductors supplied by the generator. I just don't see this being done with those type of transfer switches, do you?gfretwell said:How about 250.35(B)?
Qualified Person. One who has skills and knowledge related to the construction and operation of the electrical equipment and installations and has received safety training to recognize and avoid the hazards involved. Informational Note: Refer to NFPA 70E-2009, Standard for Electrical Safety in the Workplace, for electrical safety training requirements.ICE said:What determines who is a qualified person
You haven't met mine.jwelectric said:Qualified Person. One who has skills and knowledge related to the construction and operation of the electrical equipment and installations and has received safety training to recognize and avoid the hazards involved. Informational Note: Refer to NFPA 70E-2009, Standard for Electrical Safety in the Workplace, for electrical safety training requirements.
I don't think that a housewife would fit in here anywhere
Have you lost your mind??????????????Are you an inspector????????????ICE said:You haven't met mine.But on a serious note, it only requires a qualified person to do work on the installation. Anybody can operate it.
There is no certification for a qualified person. It could very well be that reading the installation instructions is all the training that is required.