1. ATTENTION returning members. If you are coming here from the old forum for the first time, you will need to reset you password. However, we had an email problem getting password reset links set out to a lot of the email addresses. That problem is temporarily rectified but IF you still have an issue, email me direct at info@thebuildingcodeforum.com and I will give you a temporary password.
    Dismiss Notice
  2. Welcome to the new and improved Building Code Forum. We appreciate you being here and hope that you are getting the information that you need concerning all codes of the building trades. This is a free forum to the public due to the generosity of the Sawhorses, Corporate Supporters and Supporters who have upgraded their accounts. If you would like to have improved access to the forum please upgrade to Sawhorse by clicking here: Upgrades
    Dismiss Notice

Would You Pass This? Electrical Question 1 Sept. 2018

Discussion in 'Electrical Codes' started by jar546, Sep 1, 2018.

  1. jar546

    jar546 *****istrator

    Joined:
    Oct 16, 2009
    Messages:
    5,656
    Likes Received:
    244
    OK, it really does not matter if you are on the 1999 NEC or 2017, so no need to specify.

    You are called for a final electrical inspection of an office building. It is time to inspect the emergency lighting system. The electrician proudly shows you how he put the emergency lighting on its own circuit. He trips the breaker and sure enough all of the emergency lights come on as expected.

    Is this a code compliant installation?

    *Added Info:
    There is no generator or any form of backup power
    This is an office with closed offices and doors
    There are no luminaires with built in emergency light ballasts
     
    #1 jar546, Sep 1, 2018
    Last edited: Sep 2, 2018
  2. Francis Vineyard

    Francis Vineyard Sawhorse

    Joined:
    Jan 1, 2010
    Messages:
    3,113
    Likes Received:
    415
    What's left of my memory there's an exception to have it on a separate circuit (can't remember what it is, I believe it has something to do same panel in the area and with exterior lights) but the battery backup should be on the general lighting circiut.
     
    #2 Francis Vineyard, Sep 1, 2018
    Last edited: Sep 1, 2018
  3. fatboy

    fatboy Administrator

    Joined:
    Oct 17, 2009
    Messages:
    5,471
    Likes Received:
    407
    I'd have to look it up to back it up, but our jurisdiction has always required emergency lighting be tied to a local lighting circuit.
     
  4. linnrg

    linnrg Sawhorse

    Joined:
    Mar 17, 2015
    Messages:
    286
    Likes Received:
    65
    Not in I-2 where all of this is on a life safety circuit.

    to JAR546, for office buildings, where all of the lights were the fluorescent and those emergency light were the ones with batteries - yes we usually tested the whole building by throwing the main or the lighting circuits they may be attached too. Are you trying to discuss the confusing language of 700.10 B? I say the contractor did it correct - one of several acceptable ways that it could be done.
     
  5. RJJ

    RJJ Platinum Member

    Joined:
    Oct 17, 2009
    Messages:
    2,882
    Likes Received:
    37
    I think he is referring to 700.12
     
  6. Paul Sweet

    Paul Sweet Sawhorse

    Joined:
    Oct 17, 2009
    Messages:
    976
    Likes Received:
    123
    NEC 700.12(B) says "... The branch circuit feeding the unit equipment shall be the same branch circuit as that serving the normal lighting in the area and connected ahead of any local switches. ..." The exception doesn't apply since there are closed offices and doors.
     
  7. linnrg

    linnrg Sawhorse

    Joined:
    Mar 17, 2015
    Messages:
    286
    Likes Received:
    65
    What version are you quoting from?
     
  8. RJJ

    RJJ Platinum Member

    Joined:
    Oct 17, 2009
    Messages:
    2,882
    Likes Received:
    37
    You do not need emergency lighting in the offices, only for the means of egress!
     
  9. steveray

    steveray Sawhorse

    Joined:
    Nov 25, 2009
    Messages:
    5,796
    Likes Received:
    666
    Open office area with 50 people you would....
     
  10. RJJ

    RJJ Platinum Member

    Joined:
    Oct 17, 2009
    Messages:
    2,882
    Likes Received:
    37
    Steveray: I agree! On that statement I was thinking of a common hall with office doors and office space beyond. You need 1 foot candle on all egress areas even if it is from a single office.
     
  11. Paul Sweet

    Paul Sweet Sawhorse

    Joined:
    Oct 17, 2009
    Messages:
    976
    Likes Received:
    123
    Linnrg, I'm quoting from the 2005 NEC, which is the latest hard copy we have. I think this has been in the NEC since the 70s or 80s. I hope that we can get a newer hard copy now that Virginia has finally adopted the 2015 IBC (we don't like to rush things here!)
     
  12. linnrg

    linnrg Sawhorse

    Joined:
    Mar 17, 2015
    Messages:
    286
    Likes Received:
    65
    Paul, I looked at 2005 online with NFPA but 700.12 B is Generator Set. Is your 2005 amended by Virginia? I have read all of 2008, 2011 etc. and I can not find the sentence you quoted. In the 2005 that I am reading 700.15 which is part of Division IV Emergency Systems for Lighting and Power seems to be the closest restriction and even then I am unsure. 700.12 F which is unit Equipment (specific things) does have a similar line "the branch circuit feeding the unit equipment shall be the same branch circuit as serving the normal lighting in the area and connected ahead of any switches".

    If you need a 2008 handme down I could get you that. We are now on the 2014 and the original number 700.10 B is not even in those older versions
     
  13. Paul Sweet

    Paul Sweet Sawhorse

    Joined:
    Oct 17, 2009
    Messages:
    976
    Likes Received:
    123
    I don't know where the "B" came from. It should be 700.12(F).

    I just looked up the 2017 edition on-line. It's now 700.12(F)(2)(3).
     