OK, it really does not matter if you are on the 1999 NEC or 2017, so no need to specify.
You are called for a final electrical inspection of an office building. It is time to inspect the emergency lighting system. The electrician proudly shows you how he put the emergency lighting on its own circuit. He trips the breaker and sure enough all of the emergency lights come on as expected.
Is this a code compliant installation?
*Added Info:
There is no generator or any form of backup power
This is an office with closed offices and doors
There are no luminaires with built in emergency light ballasts
You are called for a final electrical inspection of an office building. It is time to inspect the emergency lighting system. The electrician proudly shows you how he put the emergency lighting on its own circuit. He trips the breaker and sure enough all of the emergency lights come on as expected.
Is this a code compliant installation?
*Added Info:
There is no generator or any form of backup power
This is an office with closed offices and doors
There are no luminaires with built in emergency light ballasts