Robert
If you are talking about a door across the corridor, to cut down on the dead end
That is allowed, as long as on the other side, you do not create an exiting violation.
And the door shall be non-locking.
I will never understand dead end corridors and i have been a code official for 25 years.
1. I don't understand how the adding of a door across the corridor makes the exiting form this space any easier, less complicated, or simpler. If anything it may complicate things.
2. I think that dead end corridors, in a facility such as the one that has been exemplified in this post, where the occupants of this building will be very familiar with the components of the means of egress is over-regulation.
Satisfy the requirement for when two exits are required and the provisions for common path of travel and I am of the opinion you should be good to go. In most cases, at least those that i have seen or that i can conjure in my peanut sized brain, the common path of travel and dead end corridors are intimately related.
I know i am charged with enforcement of what is in the book(s) but this never sat right with me.
Of course this all goes away in high occupancy uses and where occupant are transient of in theory, "not familiar with their surroundings".
For those curious, a conversation with the plan reviewer on this topic affirmed that our proposed solution was acceptable. To be honest, I was surprised to hear him say that this was commonly done since I struggled to find much commentary or discussion on the condition.
Thank you to everyone who offered insight.