misterflippers
I live in MA, and I have recently run into problems with the building inspector and my basement which I finished without a permit. (Yes, I know, shame on me, but I was young, dumb, didn't think I needed one, etc) The basement was empty when I purchased my condo. Concrete walls, concrete floor, and two windows which measure 12"Hx32"W each.
The inspector stated that I needed to submit an application for a building permit, and then bring the basement up to current code. The inspector states that the plan submitted does not conform to building code because of R310.1, stating that I need an emergency egress in any basement, despite creating NO sleeping rooms. I created a wet bar, a home theater and a play space (that was intended for a pool table that I never actually got). All of these are one single room. No bedroom. No sleeping space.
For reference, the current code as of 2019 from https://up.codes/viewer/massachusetts/irc-2015/chapter/3/building-planning#R310:
R310.6 Alterations or Repairs of Existing Basements
An emergency escape and rescue opening is not required where existing basements undergo alterations or repairs.
Exception: New sleeping rooms created in an existing basement shall be provided with emergency escape and rescue openings in accordance with Section R310.1.
His response was that "if you built a finished basement in the 1950's, and then wanted to remodel it, we're not going to make you suddenly need an egress. It does not apply when going from uninhabitable to habitable space."
Since then, I have been trying to find commentary, discussion, or clarification on this.
Within the IRC, the term basement is defined as any story below grade. It says NOTHING about habitable space, finished, or otherwise. I have checked the amendments for MA, and MA does not amend R310.1 or R310.6 in any way from the IRC.
So, if I am reading R310.6, alteration to an existing basement, which is any story below grade, finished or unfinished, is exempt from this requirement unless you add a bedroom.
Is there any sort of clarification or commentary on this anywhere? Otherwise, I feel like this interpretation is unfair (currently to the tune of about $25,000).
R310.1 Emergency Escape and Rescue Opening Required
Basements, habitable attics and every sleeping room shall have not less than one operable emergency escape and rescue opening. Where basements contain one or more sleeping rooms, an emergency escape and rescue opening shall be required in each sleeping room. Emergency escape and rescue openings shall open directly into a public way, or to a yard or court that opens to a public way.
So, I asked him why R310.6 does not apply to my situation. Reference of the text for R310.6:Basements, habitable attics and every sleeping room shall have not less than one operable emergency escape and rescue opening. Where basements contain one or more sleeping rooms, an emergency escape and rescue opening shall be required in each sleeping room. Emergency escape and rescue openings shall open directly into a public way, or to a yard or court that opens to a public way.