My building is subdivided with a firewall so each compartment is approx. 440 sq.m. and is 3 storeys. There are two exits stairs , on each corner. Can i give an exit stair in the center of both buildings as a shared exit stair?
Your premier resource for building code knowledge.
This forum remains free to the public thanks to the generous support of our Sawhorse Members and Corporate Sponsors. Their contributions help keep this community thriving and accessible.
Want enhanced access to expert discussions and exclusive features? Learn more about the benefits here.
Ready to upgrade? Log in and upgrade now.
Each building has one exit stair.Yes...Probably...Do they have other exits?
Type of occupancy?My building is subdivided with a firewall so each compartment is approx. 440 sq.m. and is 3 storeys. There are two exits stairs , on each corner. Can i give an exit stair in the center of both buildings as a shared exit stair?
Missed that....Concept is sound, but not familiar with Canada specifics...Each building has one exit stair.
Type of occupancy is residential.Type of occupancy?
Why is the firewall there??
What is the rating??
May take someone from up north to answer the question
Type of occupancy is residential.
Firewall is given to sub-divide the building so it fall under the category which allow combustible construction.
It is just concept now in schematic design stage. They do allow horizontal exit.so is this built or concept?
Does up north have horizontal exit provisions
It is just concept now in schematic design stage. They do allow horizontal exit.
More complicated than what? Once you have the firewall all you need is refuge area and a standpipe.A horizontal exit is a lot more complicated than that...
I might not have been clear enough...
On each side of the firewall you just need one set of stairs and a door through the firewall to the building on the other side.
Well, assuming it is a true firewall, not just a fire separation, it would be acceptable provided it is a minimum of 2 hours rating. If it is not constructed out of concrete or masonry, the fire resistive elements need to be protected from damage. Also needs to meet the structural requirements of a firewall.Need more info from the poster
Rating on the wall
how many units on each side
etc.....
And the other half are ... vertical exits?. The only restriction is that a horizontal exit cannot account for more than half of the exits.
Other acceptable exits are...And the other half are ... vertical exits?
Those requirements are for I occupancies, OP stated it was residential.Two way communication....An additional smoke barrier unless the AOR is in the stair, and if that is the case, a large landing....Whatever else I am not thinking of right now...
So it is your position that a refuge area is not an area of refuge?Those requirements are for I occupancies, OP stated it was residential.
Horizontal exits are really straightforward (under IBC) and are a very common MOE for buildings separated by fire walls.
So it is your position that a refuge area is not an area of refuge?
1026.4 Refuge area. The refuge area of a horizontal exit
shall be a space occupied by the same tenant or a public area
and each such refuge area shall be adequate to accommodate
the original occupant load of the refuge area plus the occupant
load anticipated from the adjoining compartment. The
anticipated occupant load from the adjoining compartment
shall be based on the capacity of the horizontal exit doors
entering the refuge area.
1009.6 Areas of refuge. Every required area of refuge shall
be accessible from the space it serves by an accessible means
of egress.
1009.6.1
1009.6.4 Separation. Each area of refuge shall be separated
from the remainder of the story by a smoke barrier
complying with Section 709 or a horizontal exit complying
with Section 1026. Each area of refuge shall be
designed to minimize the intrusion of smoke.
Exceptions:
1. Areas of refuge located within an enclosure for
interior exit stairways complying with Section
1023.
2. Areas of refuge in outdoor facilities where exit
access is essentially open to the outside.
1009.6.5 Two-way communication. Areas of refuge shall
be provided with a two-way communication system complying
with Sections 1009.8.1 and 1009.8.2.
AREA OF REFUGE. An area where persons unable to use
stairways can remain temporarily to await instructions or
assistance during emergency evacuation.\