Can two buildings divided by firewall share a common exit stair?

AreaArch

REGISTERED
Joined
Mar 8, 2021
Messages
4
Location
Toronto, Ontario
My building is subdivided with a firewall so each compartment is approx. 440 sq.m. and is 3 storeys. There are two exits stairs , on each corner. Can i give an exit stair in the center of both buildings as a shared exit stair?
 
My building is subdivided with a firewall so each compartment is approx. 440 sq.m. and is 3 storeys. There are two exits stairs , on each corner. Can i give an exit stair in the center of both buildings as a shared exit stair?
Type of occupancy?

Why is the firewall there??

What is the rating??

May take someone from up north to answer the question
 
Type of occupancy?

Why is the firewall there??

What is the rating??

May take someone from up north to answer the question
Type of occupancy is residential.
Firewall is given to sub-divide the building so it fall under the category which allow combustible construction.
 
Type of occupancy is residential.
Firewall is given to sub-divide the building so it fall under the category which allow combustible construction.

so is this built or concept?



Does up north have horizontal exit provisions
 
Sounds like a horizontal exit under IBC. You may not need the center stair, the exit is at the firewall if you meet the horiz exit requirements.
 
Two way communication....An additional smoke barrier unless the AOR is in the stair, and if that is the case, a large landing....Whatever else I am not thinking of right now...
 
Just to clarify, under the Canadian codes, this would still be considered a horizontal exit. The exit is the door in the firewall. Theoretically, if one building is on fire on one side of the firewall, the firewall will prevent the fire from spreading to the other side of the building. The only restriction is that a horizontal exit cannot account for more than half of the exits. In this case, assuming two is necessary for the floor area, this is acceptable.

See 3.4.1.6 in the OBC
 
I might not have been clear enough...

On each side of the firewall you just need one set of stairs and a door through the firewall to the building on the other side.
 
I might not have been clear enough...

On each side of the firewall you just need one set of stairs and a door through the firewall to the building on the other side.


Need more info from the poster

Rating on the wall

how many units on each side

etc.....
 
Need more info from the poster

Rating on the wall

how many units on each side

etc.....
Well, assuming it is a true firewall, not just a fire separation, it would be acceptable provided it is a minimum of 2 hours rating. If it is not constructed out of concrete or masonry, the fire resistive elements need to be protected from damage. Also needs to meet the structural requirements of a firewall.

The number of units, or occupant load for that matter, does not restrict the use of horizontal exits.
 
And the other half are ... vertical exits?
Other acceptable exits are...

exterior doorway
exterior passageway
exterior ramp
exterior stairway
a fire escape (must conform to 3.4.7. which does not allow them for new buildings)
an interior passageway
an interior ramp
an interior stairway

in this case, they have an interior stairway that is their other half.
 
Two way communication....An additional smoke barrier unless the AOR is in the stair, and if that is the case, a large landing....Whatever else I am not thinking of right now...
Those requirements are for I occupancies, OP stated it was residential.

Horizontal exits are really straightforward (under IBC) and are a very common MOE for buildings separated by fire walls.
 
Those requirements are for I occupancies, OP stated it was residential.

Horizontal exits are really straightforward (under IBC) and are a very common MOE for buildings separated by fire walls.
So it is your position that a refuge area is not an area of refuge?

1026.4 Refuge area. The refuge area of a horizontal exit
shall be a space occupied by the same tenant or a public area
and each such refuge area shall be adequate to accommodate
the original occupant load of the refuge area plus the occupant
load anticipated from the adjoining compartment. The
anticipated occupant load from the adjoining compartment
shall be based on the capacity of the horizontal exit doors
entering the refuge area.

1009.6 Areas of refuge. Every required area of refuge shall
be accessible from the space it serves by an accessible means
of egress.
1009.6.1

1009.6.4 Separation. Each area of refuge shall be separated
from the remainder of the story by a smoke barrier
complying with Section 709 or a horizontal exit complying
with Section 1026. Each area of refuge shall be
designed to minimize the intrusion of smoke.
Exceptions:
1. Areas of refuge located within an enclosure for
interior exit stairways complying with Section
1023.
2. Areas of refuge in outdoor facilities where exit
access is essentially open to the outside.
1009.6.5 Two-way communication. Areas of refuge shall
be provided with a two-way communication system complying
with Sections 1009.8.1 and 1009.8.2.

AREA OF REFUGE. An area where persons unable to use
stairways can remain temporarily to await instructions or
assistance during emergency evacuation.
 
So it is your position that a refuge area is not an area of refuge?

1026.4 Refuge area. The refuge area of a horizontal exit
shall be a space occupied by the same tenant or a public area
and each such refuge area shall be adequate to accommodate
the original occupant load of the refuge area plus the occupant
load anticipated from the adjoining compartment. The
anticipated occupant load from the adjoining compartment
shall be based on the capacity of the horizontal exit doors
entering the refuge area.

1009.6 Areas of refuge. Every required area of refuge shall
be accessible from the space it serves by an accessible means
of egress.
1009.6.1

1009.6.4 Separation. Each area of refuge shall be separated
from the remainder of the story by a smoke barrier
complying with Section 709 or a horizontal exit complying
with Section 1026. Each area of refuge shall be
designed to minimize the intrusion of smoke.
Exceptions:
1. Areas of refuge located within an enclosure for
interior exit stairways complying with Section
1023.
2. Areas of refuge in outdoor facilities where exit
access is essentially open to the outside.
1009.6.5 Two-way communication. Areas of refuge shall
be provided with a two-way communication system complying
with Sections 1009.8.1 and 1009.8.2.

AREA OF REFUGE. An area where persons unable to use
stairways can remain temporarily to await instructions or
assistance during emergency evacuation.\




"""So it is your position that a refuge area is not an area of refuge?""""



That is a true statement. I got schooled on that. Not sure why the code writer's god, uses similar terms
 