I have high rise and hospital building which has Fire Smoke dampers. Should the Fire Smoke Dampers (FSD) be installed in emergency circuit or standby circuit or equipment circuit?
Your premier resource for building code knowledge.
This forum remains free to the public thanks to the generous support of our Sawhorse Members and Corporate Sponsors. Their contributions help keep this community thriving and accessible.
Want enhanced access to expert discussions and exclusive features? Learn more about the benefits here.
Ready to upgrade? Log in and upgrade now.
They for the duct detector/smoke damper. The fire smoke dampers are installed in the mechanical duct. The mechnical ducts in which they are placed in serve both a corridor and shell space.Do you have to comply with NFPA 101 and I Codes???
Part of a smoke removal system?????????????
Not my area, but seems like, depending on where they are in the building, might just be part of the defend in place system, and you would want them to actuate, or fail to the desired postion, for the defend in place/ smoke compartments
Part of a smoke removal system?????????????
Your MechE will know. Your MechE and EE should be able to answer all of your questions.How can you tell if it is or it is not? Project focuses on part of area of building??
Ok I will ask them is damper part of smoke removal system or not and get back to youYour MechE will know. Your MechE and EE should be able to answer all of your questions.
Part of a smoke removal system?????????????
Now what?
Yes. The Fire Smoke Damper is installed where dict penetrate the wall which is fire rated.Ask the mechanical Engineer.
This is a true high rise, and hospital in one???
Yes. The Fire Smoke Damper is installed where dict penetrate the wall which is fire rated.
So in order to maintain the Fire or Smoke rating the fire smoke damper is installed.
The air handler unit is also on equipment branch.
When their is a smoke the smoke detector signal fire alarm control panel which then signal the damper shut. Even when generator kick in equipment branch if their is smoke the dampers would be shut by the fire alarm control panel.
So what do you thin in terms of being in equipment branch or emergency branch?
When power is lost and no generator involved the dampers are shut.Ok last question
No generator involved
If they loose power,,, do they fail open or shut???
Dampers shut when their is no power. I just want to know should they be on equipment branch or emergency branch for high rise hospital building?I believe there are two types of smoke only dampers (as opposed to combination fire and smoke dampers); those held open under normal power which close upon loosing power; and those which require emergency power to close.
I'm not understanding your position in this and why the electrical engineer and mechanical engineer are not coordinating this. They do - or did since I'm retired - on projects I consulted on.
If you know what dampers are being specified, I suggest looking at their installation manual and/or calling that manufacturer's tech support. Much more reliable than an internet bulletin board.
The really hard part of smoke dampers seems to be the periodic testing and assuring there is access.
Well I answered your question. No response came?Ok last question
No generator involved
If they loose power,,, do they fail open or shut???
Well I answered your question. No response came?
I dont get it which one equipment branch or life and safety branch? This is hospital high rise and their is no emergency branchDampers shut when their is no power. I just want to know should they be on equipment branch or emergency branch for high rise hospital building?
Sounds like that is the answer
Other than ask the mechanical engineer, which is what I would do.
How are you connected with all this,,,? What is your job
SorryI dont get it which one equipment branch or life and safety branch? This is hospital high rise and their is no emergency branch
Ok I still dont get it. How is that the answer to would the dampers motors be on equipment branch or life and safety branch? Please elaborate furtherSorry
Dampers shut when their is no power
Plus ask the Mech Engineer
Ok I still dont get it. How is that the answer to would the dampers motors be on equipment branch or life and safety branch? Please elaborate further
ReviewerTo better approach the answer
How are you connected with the project??
What do you do for a living
Yet another question to your last question. I answered that and yet another pin silent. No response to my questionTo better approach the answer
How are you connected with the project??
What do you do for a living
Yet another question to your last question. I answered that and yet another pin silent. No response to my question