I have an existing office building with five stories above ground floor, not fully sprinklered, and its main exit stairway discharges through the ground floor lobby which doubles up as the main entrance.
There is a desk with a couple security guards at the lobby and the 800 sqf lobby is sprinklered and separated 2h from the rest of the building which is not sprinklered except from a basement 15 place car park.
It complies with the exception in Section 1028.1, but my question on finishes requirements for this lobby. Which column in table 803.1 is applicable? I presume we are looking at the "sprinklered" columns since the title is not "fully sprinklered", right?
Then, do we go for class B since this is continuation of the exit stairway, or C for corridors?