This is a screen shot of the CALBO training material. The indication is that a service panel that does not have a single disconnect is not legal. According to this, no longer can you have a service with up to six circuit breakers serving as the service disconnect if it is in a single enclosure/cabinet.

20221015_095710.jpg
 
The condition that's no longer approved that common? At least around here I don't believe I've ever seen it.
It is found in older service applications as well as contemporary feeder supplied detached structures.

The CALBO training material might be incorrect....

I was also informed that there will not be a PDF version of the California Electrical Code.... only printed. That's awful.
 
Last edited:
It was a way to avoid spending a bunch of money to comply with NEC 230.95. Instead of buying a 1000A or larger GFP main breaker we would have up to 6 smaller breakers in one main lug panel board as our service equipment.
Around here we usually see the configuration on the far right for multiunit buildings.
 
It is found in older service applications as well as contemporary feeder supplied detached structures.

The CALBO training material might be incorrect....

I was also informed that there will not be a PDF version of the California Electrical Code.... only printed. That's awful.

It is correct, although I believe you can have 6 separate disconnects in the same cabinet as long as they are separated/guarded from each other, so you can access the wiring to each disconnect without being exposed the wiring for the others.
 
Almost every island/penisala will require multiple receptacles..

20221017_130942.jpg


Are you people paying attention?
 

Attachments

  • 20221017_130942.jpg
    20221017_130942.jpg
    2 MB · Views: 54
Last edited:
20221017_131240.jpg

Decks are mentioned here. Jeff is excited about decks.
 
Last edited:
Just starting the 2017 NEC here and still electrical contractors don't know about the 2014 requirement for 110.24 available fault current label for the service. I have been just requiring it on large services above 200A or 3 phase so far. Wonder if everyone else requires it on small and temporary services?
They don't seem to know about "extra duty" in use covers over outdoor receptacles too.
 
Joe pinching pennies?
Considering the breadth of your code knowledge perhaps you can shed light on what drove the code change. There is not an apparent advantage to the new code and the old code has been around for a long time. The reason is probably written down somewhere and if anyone knows where....you do.

Thanks
 
I was also informed that there will not be a PDF version of the California Electrical Code.... only printed. That's awful.
It (2019 and 2023) is online:
 
2023 NEC No longer requires island or peninsula receptacles, but id you have them they have to be above the top of the counter...
Here is the 2023 NEC. Note that the code says if installed it shall be on or above the countertop. It goes on to say that if a receptacle is not provided it shall be installed anyway.

It makes me wonder if the committee members came to blows before they reached this impasse.

20221018_143920.jpg
 
Last edited: