Outdoor Receptacles Outlets and NEC 210.52(E)
Outdoor receptacles must be installed so that the receptacle faceplate rests securely on the supporting surface to prevent moisture from entering the enclosure. On uneven surfaces such as brick, stone, or stucco, it might be necessary to use mounting blocks or to close openings with caulking compound or mastic.
See NEC 406.9 for more information on receptacles installed in damp or wet locations if you don't agree with the above statement.
2020 NEC
406.9(E) Flush Mounting with Faceplate.
The enclosure for a receptacle installed in an outlet box flush-mounted in a finished surface shall be made weatherproof by means of a weatherproof faceplate assembly that provides a watertight connection between the plate and the finished surface.
I don’t see a mention of caulk or mastic. Now if the code said make a mess of it …. Well then, spuge away.
We have an inspector locally that doesn't allow NM to exterior fixtures because it is a "wet location"....Which is what this section seems to be attempting to avoid....
2020 NEC
It says watertight connection. I think it was worded that way to allow more than one sealing method. Foam strip on the bsck of the plate. Skillfully and neatly applied caulk.
Caulk is a sacrificial building component. As long as you are willing to replace it every few years it will perform. As an inspector I don’t trust that it will happen so I ask for a permanent building component. The rubber washer is one method….doubled up even.