Handrail safety terminal
Yes Mark, no one is saying they don't but when and why was they handrail termination put under the microscope....in the model codes
But that is exactly what we do as Building Official, Put things under the microscope and try to figure out the verbiage and the intent of the code.
Per the original question, is it in the residential code, yes
R311.7.8.4 Continuity
Handrails shall be continuous for the full length of the flight, from a point directly above the top riser of the flight to a point directly above the lowest riser of the flight. Handrail ends shall be returned toward a wall, guard walking surface continuous to itself, or terminate to a post.
Just a small correction here. The 2018 IRC as I see it reads:
Handrails shall be continuous for the full length of the flight, from a point directly above the top riser of the flight to a point directly above the lowest riser of the flight. Handrail ends shall be returned or shall terminate in newel posts or safety terminals.
Depends on Version of code you are using, not everyone is under the same code.
So Yankee,
Please explain how you believe none of the posted handrail terminations you flagged are not compliant with the IRC and specifically highlighting prior to 2021 model IRC and post 2021, Remember the OP is asking about 2018 IRC.
For the record, none of the pictures were on flights that required guards.
He may have been talking about the HR themselves...do they meet the type II 6-1/4" perimeter and that stuff?
Geometry class all over again. It's a bit of a surprise when you learn that one size fits all.
R311.7.8.5 Grip size. Required handrails shall be of one of the following types or provide equivalent grasp-ability.
1. Type I. Handrails with a circular cross section shall have an outside diameter of not less than 11/4inches and not greater than 2 inches. If the handrail is not circular, it shall have a perimeter of not less than 4 inches and not greater than 61/4 inches and a cross section of not more than 21/4 inches. Edges shall have a radius of not less than 0.01 inch.
2. Type II. Handrails with a perimeter greater than 61/4 inches shall have a graspable finger recess area on both sides of the profile. The finger recess shall begin within 3/4 inch measured vertically from the tallest portion of the profile and have a depth of not less than 5/16 inch within 7/8 inch below the widest portion of the profile. This required depth shall continue for not less than 3/8 inch to a level that is not less than 13/4 inches below the tallest portion of the profile. The width of the handrail above the recess shall be not less than 11/4 inches and not more than 23/4inches. Edges shall have a radius of not less than 0.01 inch.
All (4) of the handrail profiles shown in my post #8 of the thread are compliant for type I handrail ("not Circular")
and (2) of the profiles where specifically provided to the Access-Board back sometime between 2002-2004 by me personally during the hearings putting for the model that there published 2004 handrail requirements meet. So I am very confident on the handrail profiles in that manner.
They are all residential terminations and the terminations have been covered under the safety terminal description for decades....
So Yankee,
I said the handrails are not compliant, not the terminations. Is the 2012 IRC old enough for you?
R311.7.8.3 Grip-size. All required handrails shall be of
one of the following types or provide equivalent graspability.
shall have an outside diameter of at least 11/4
inches (32 mm) and not greater than 2 inches (51
mm). If the handrail is not circular, it shall have a
perimeter dimension of at least 4 inches (102
mm) and not greater than 61/4 inches (160 mm)
with a maximum cross section of dimension of
21/4 inches (57 mm). Edges shall have a minimum
radius of 0.01 inch (0.25 mm).
61/4 inches (160 mm) shall have a graspable finger
finger recess shall begin within a distance of 3/4
inch (19 mm) measured vertically from the tallest
portion of the profile and achieve a depth of at
least 5/16 inch (8 mm) within 7/8 inch (22 mm)
required depth shall continue for at least 3/8 inch
(10 mm) to a level that is not less than 13/4 inches
(45 mm) below the tallest portion of the profile.
The minimum width of the handrail above the
recess shall be 11/4 inches (32 mm) to a maximum
of 23/4 inches (70 mm). Edges shall have a minimum
There's nothing in any of the photos to allow scaling the profiles, but most look like standard metal handrails that shops all across the country produce and sell -- and the ones I see don't meet the code requirements for profile.
Have you ever done a complete handrail profile review, your assumption that they don't comply could be wrong, by looking at pictures.
All the profiles of the handrails in post #8 comply with not only 2012 IRC, 2012 IBC, A117.1 and 2010ADA (2004 Access-Board Model Standard).
yes.
That's why we don't use pictures for code enforcement.
There is no way to know that from the photos.
"...or provide equivalent grasp-ability."
I appreciate this little clause because it allows the Building Official to accept alternatives.
True, but are many building officials trained to judge graspability? How many can judge what an arthritic hand can grasp? Do they even understand a hook grip, the most important for falls in decent?
I just wonder if it's fair of the code to expect that kind of expertise of every enforcer using the code.