Second question - Does a space allocated for storage or office supplies qualify as an occupiable area, and therefore, should it be considered in this calculation if it's the furthest room?Are there more specific instructions on how to measure this distance apart from this definition? For example, if you have a corridor that is 8' wide, does your measurement line need to be in the center, or can it be a certain distance from the wall?
YesSecond question - Does a space allocated for storage or office supplies qualify as an occupiable area, and therefore, should it be considered in this calculation if it's the furthest room?
I understood that for "Exit Access Travel Distance," but I wasn't sure if it also applies to "Common Path of Travel Distance." Regardless, it seems quite vague to me. Perhaps I'm overthinking it.1017.3 Measurement.
Exit access travel distance shall be measured from the most remote point of each room, area or space along the natural and unobstructed path of horizontal and vertical egress travel to the entrance to an exit.
It is always open to some interpretation...but if you measure it at right angles, you are never wrong unless you create a dead end with furnishings or something odd...along the natural and unobstructed path of horizontal and vertical egress travel
When measuring travel distance, it is important to consider the natural path of exit access travel [see Commentary
Figure 1017.3(1)]. In many cases, the actual layout of furnishings and equipment is not known or is not identified
on the plans submitted with the permit application. In such instances, it may be necessary to measure travel
distance using the legs of a right triangle instead of the hypotenuse [see Commentary Figure 1017.3(2)]. Since
most people tend to migrate to more open spaces while egressing, measurement of the natural path of exit
access travel typically excludes floor areas within 1 foot (305 mm) of walls, corners, columns and other permanent
construction. Where the travel path includes passage through a doorway, the natural route is generally
measured through the centerline of door openings.
Sometimes checking the definitions will help you when over thinking somethingI understood that for "Exit Access Travel Distance," but I wasn't sure if it also applies to "Common Path of Travel Distance." Regardless, it seems quite vague to me. Perhaps I'm overthinking it.
Check out this video on CPET:Are there more specific instructions on how to measure this distance apart from this definition? For example, if you have a corridor that is 8' wide, does your measurement line need to be in the center, or can it be a certain distance from the wall?