Mr. Inspector
Is the designer required to say what method they are using in the IEBC when replacing or adding a sign on the outside of an existing building?
The alteration, addition or change of occupancy of all existing buildings shall comply with one of the methods listed in Section 301.3.1, 301.3.2 or 301.3.3 as selected by the applicant. Sections 301.3.1 through 301.3.3 shall not be applied in combination with each other.
Adding or replacing a sign is not within the scope of the IEBC.
[A] 101.2 Scope.
The provisions of this code shall apply to the repair, alteration, change of occupancy, addition to and relocation of existing buildings.
Right about here:Yes, and if you look at the definitions of "repair," "alteration," "change of occupancy," and "addition," where do you find anything that would include an exterior, building-mounted sign in its scope?
What else would it be? A sign. In over 50 years of practice I have never encountered a sign being construed as an alteration. It's a sign.Yes, and if you look at the definitions of "repair," "alteration," "change of occupancy," and "addition," where do you find anything that would include an exterior, building-mounted sign in its scope?
Seems plain to me that adding a sign is an alteration. What else would it be?
And where would you find any requirements in the IEBC for what is required to meet code?
When the IEBC is silent on a specific subject then you need to move to a code that would be applicable.
Appendix H of the IBC, needed to clarify that.Appendix H if adopted