XE1805
Have a question about continuity of a 2 hr fire separation where a group C Residential occupancy sits on top of a Group F2 Industrial Occupancy. Basically putting an apartment above an F2 fabrication shop. See attached section sketch of the situation.
Existing F2 shop, wood framed, 2 storey, no sprinkler, all combustible framing. Project is to add an extension to the shop off the back wall of the ground floor, and then put a single apartment above. NBCC Occupancy matrix says a 2hr fire separation required between those 2 occupancies. Final building will likely be just over 600sm in building area.
It's clear the that the floor between the apartment and the shop extension needs to be rated. What is less clear is if the vertical exterior wall of the apartment that sits above the shop also needs the same rating if the existing adjacent roof is combustible and not rated.
I am looking for some specific NBCC code references that apply in this situation. 3.1.7.3(3) says 'Exterior walls shall be rated from exposure to fire from inside the building.' which would not be the case here. Have not yet investigated the need for sprinklers.
thanks
thanks