Recently got a comment from an inspector that I'm struggling to rationalize fully. I'm probably reading too much into it, but I'm hoping you fine folks can help clarify the requirements they're referencing.
2022 California Building Code. Project is an existing commercial building. Permit was issued before the California Existing Building Code got major alterations, so that code isn't very applicable here.
There's an existing exterior door we're planning on using as the accessible entry (CBC 11B-202.4). I'm being told that, due to CBC 1010.1.4 and 11B-404.2.4, we need a level landing (<2% slope) on the interior side of the door. All well and fine, but the part I'm confused about is 11B-404.2.4 in regards to the interior side of an entry door.
The issue is not about egress according to the inspector. The issue is about the path of travel to the space. They're saying that the maneuvering clearance required by Table 11B-404.2.4.1 is required on both sides of the door when entering a space. If maneuvering clearances are required, then a <2% slope is required within that maneuvering clearance (11B-404.2.4.4). Essentially, they're asking for the push and pull side maneuvering clearance when the approach is only from the pull side (exterior side).
I thought that the maneuvering clearances only apply on the approach side. I completely understand that most doors have maneuvering clearances on both sides since most doors can be operated from both sides, but that's apparently not the concern that triggered this comment.
They're adamant on this, which makes me think I'm simply missing something or interpreting code wrong.
I have no complaints about fixing the issue. I'd prefer it fixed anyways. I more just interested in how these sections of code apply to this situation, because I'm reading code differently than the inspector.
Also, 11B-207.1, exception 3 says that accessible means of egress are not required in existing buildings. Would an existing building undergoing an interior alteration with no new exterior doors meet this exception? Inspector says this is no longer an existing building, so I'm hoping to get some clarity on that too.
2022 California Building Code. Project is an existing commercial building. Permit was issued before the California Existing Building Code got major alterations, so that code isn't very applicable here.
There's an existing exterior door we're planning on using as the accessible entry (CBC 11B-202.4). I'm being told that, due to CBC 1010.1.4 and 11B-404.2.4, we need a level landing (<2% slope) on the interior side of the door. All well and fine, but the part I'm confused about is 11B-404.2.4 in regards to the interior side of an entry door.
The issue is not about egress according to the inspector. The issue is about the path of travel to the space. They're saying that the maneuvering clearance required by Table 11B-404.2.4.1 is required on both sides of the door when entering a space. If maneuvering clearances are required, then a <2% slope is required within that maneuvering clearance (11B-404.2.4.4). Essentially, they're asking for the push and pull side maneuvering clearance when the approach is only from the pull side (exterior side).
I thought that the maneuvering clearances only apply on the approach side. I completely understand that most doors have maneuvering clearances on both sides since most doors can be operated from both sides, but that's apparently not the concern that triggered this comment.
They're adamant on this, which makes me think I'm simply missing something or interpreting code wrong.
I have no complaints about fixing the issue. I'd prefer it fixed anyways. I more just interested in how these sections of code apply to this situation, because I'm reading code differently than the inspector.
Also, 11B-207.1, exception 3 says that accessible means of egress are not required in existing buildings. Would an existing building undergoing an interior alteration with no new exterior doors meet this exception? Inspector says this is no longer an existing building, so I'm hoping to get some clarity on that too.